RPM command execution delay

Hi,

We are using RPM to configure our ups's. We have several W2k machines but also some non-windows machines (unix, netapp filer). On these machines I cannot install the agent software to control shutdown. I want to execute a command with a 10 minute delay, that shutdowns for example a unix server when the UPS goes on battery. In RPM the delay can be set, but what happens when utility power is restored within the delay period. Will the command still be executed or will it be aborted ?

TIA
Eelco
1 REPLY 1
Bill Place_1
Frequent Advisor

Re: RPM command execution delay

Eelco

Commands are initiated as soon as the event configured is triggered. i.e. the 10 minutes delay clock starts. Once initiated HPRPM will not abort.