BL P-Class server power issue

Andy Orthun
Occasional Visitor

BL P-Class server power issue

My BL P-Class server power supplies are having an issue. I have 2 power inclosures with 4 x 3 Phase 220 going in.

The bottom right 3 power supplies (4,5,6) show "Check Input" when viewing them through the ILO of one of the servers. I checked the Power comming out of the recepticle and its good.

If all power supplies that I've tested are installed in bays 4,5,6 the chassis still shows as them as not powered on and to check input.

Andy
2 REPLIES
Lawrance Lee_1
Frequent Advisor

Re: BL P-Class server power issue

Are you sure that the 3 phase power is correctly wired for the power supplies 4, 5 & 6? Being 3 phase, it may be possible that the wiring was not done correctly. Have you tried plugging in the side with power supply modules 1, 2 & 3 into the circuit which is feeding 4, 5 & 6?

Have you logged in to the management module at the back of the 3U power enclosure?

You will need a 9 pin serial cable and a computer (laptop) that has a serial port in order to view the logs on the management module. It might explain why you are seeing this error message. I have not come across this error message before.



Andy Orthun
Occasional Visitor

Re: BL P-Class server power issue

Fixed the problem - It turns out that the power enclosure was bad! Replaced it and everything works!

Thanks,

Andy