BL460 Power Enclosure Error

 
Dave Zegen
Occasional Visitor

BL460 Power Enclosure Error

Recently we've started getting notifications in event viewer with the following error:

Machine Environment : Power Enclosure Overheating (Zone 2, Location Power Supply, Temperature 201C, Enclosure Address FC97)

10 seconds later it seems to resolve itself and sends out a second notifier:

NOTE: This event indicates that the following situation, which was previously logged as an error, has been REPAIRED and is no longer a problem.

3 REPLIES 3
Dave Zegen
Occasional Visitor

Re: BL460 Power Enclosure Error

Update:

Here is an email notification we recieve-

Title: cpqRackPowerSubsystemLineVoltageProblem

Trap Description: "The rack power supply detected an input line voltage problem.

User Action: Check the power input for the power supply or replace any failed power supplies as soon as possible."
Service Action:
The power supply at position 1 of power supply enclosure Unknown has suffered a loss of line voltage. Inspect power supply connections and take necessary action to restore power.

Failing Part:
Power Supply Position: 1
Power Supply Enclosure: Unknown

Failing Part Location:
The power supply that lost line voltage is installed at position 1 of power supply enclosure Unknown in the rack enclosure Unknown a ProLiant BL20p G3 with serial number USM52602H4.

Service Notes:


Power Supply Spare Part #: undefined
Power Supply Position: 1
Power Supply Enclosure: Unknown

Rack Enclosure Model #: ProLiant BL20p G3
Rack Enclosure Name: Unknown
Rack Enclosure Serial #: M019NFH14W
Rack Enclosure ProductID: 380634-B21
Rack Enclosure FW Rev: undefined
Jimmy Vance
HPE Pro

Re: BL460 Power Enclosure Error

So are you dealing with power error messages from 2 different enclosures? Your thread title is for a BL460, your second message looks to be from the older enclosures for the BL20p. BL460 and BL20p servers use different enclosures
No support by private messages. Please ask the forum! Accept or KudoI work for HPE
Blazhev_1
Honored Contributor

Re: BL460 Power Enclosure Error

Hi,

this is known issue with the p-class management module firmware

http://h20000.www2.hp.com/bizsupport/TechSupport/SoftwareDescription.jsp?lang=en&cc=us&prodTypeId=3709945&prodSeriesId=397630&swItem=MTX-9e0e8e80b2d545eeaa26c38678&prodNameId=3288174&swEnvOID=1005&swLang=8&taskId=135&mode=5


Check revision history (Fixes) :

Enhanced error detection algorithm to prevent false power enclosure overheating messages from being posted in the IML log on 1U power enclosures.
Caution: Machine Environment: "Power Enclosure Overheating (Zone X, Location Power Supply, Temperature xxxC, Enclosure Serial Number xxxxxxxxxx"
Repaired: Machine Environment: "Power Enclosure Overheating (Zone X, Location Power Supply, Temperature 0C, Enclosure Serial Number xxxxxxxxxx"

Update and error will go away