BladeSystem - General
1752600 Members
4665 Online
108788 Solutions
New Discussion

Re: C3000 enclosure with 4 * BL460c GEN8 and 3 * BL460C GEN10

 
SOLVED
Go to solution
JooKal
Occasional Advisor

C3000 enclosure with 4 * BL460c GEN8 and 3 * BL460C GEN10

We have a problem with a C3000 enclosure and 4 * BL460C GEN8 and 3 * BL460c GEN10
If I have the GEN8 server on.
I can turn two GEN10 servers on without problems but if the third GEN10 server power on,
two of the three GEN10 servers go power off with a Device Operational Error power off.
In the IML log we get the following message
Rack Infrastructure 07/16/2019 13:26:43 07/16/2019 13:26:43
1 Server Blade Enclosure Power Request Denied: Enclosure Busy
(Enclosure Serial Number Cxxxxxxxx, Bay 2)

OA firmware is 4.90 power managemeent 1.04 feb 2019.
The question is is this supported configuration or have we a other problemen.
The customer uses multiple C3000 with 6* GEN8 and 2* GEN10 servers without problems

 

 
 

 

2 REPLIES 2
KBSingh
HPE Pro

Re: C3000 enclosure with 4 * BL460c GEN8 and 3 * BL460C GEN10

Hi

This is an identified issue and HPE Engineering is working on it.

However, the solution is not yet validated. Please raise a support case with HPE Support.

once you have a support case, we should be able to track the issue and share the fix.

Thank you

Regards

KB

 


Accept or Kudo
JooKal
Occasional Advisor
Solution

Re: C3000 enclosure with 4 * BL460c GEN8 and 3 * BL460C GEN10

HPE have swape the backplane of the C3000 en closure and the customer is now running the GEN10 server for over 3 weeks without anny problems.

The following parts are installed

 708050-001 R2 midplane board
Part 441829-001 is no longer supplied. Please order the replacement, 708050-001

Problem solved