BladeSystem - General
1753943 Members
9170 Online
108811 Solutions
New Discussion юеВ

Re: C7000 Flex 10 virtual connect fiber channel

 
SOLVED
Go to solution
Le Coq Manuel
Frequent Advisor

C7000 Flex 10 virtual connect fiber channel

hello,
I am installing two chassis C7000 with Virtual Connect Fibre Channel. I will install the ESXi 4.1 on the BL460 G7 blade. I wish to boot from SAN. I create profiles. Each blade has two fiber channel card, I turned and I filled a WWPN in primary and secondary in the profile.But I have a random operation. So I checked the zonning point to point is good.On one slide I have two, one or zero path.I checked the NPVI is active on the ports of my fiber switches. In contrast, in virtual connect when I look at the status of the fiber card fiber channel module I have not logged in when I'm missing paths.For me the problem just the relationship between the blade and the Virtual Connect Fibre Channel Module. Attached is a screen, the four blades are started and have the same profile configuration. And yesterday before the blade stopping it worked.
I also opened a box from HP.

Cordially
16 REPLIES 16
Johan Guldmyr
Honored Contributor

Re: C7000 Flex 10 virtual connect fiber channel

It won't say logged in unless the OS has loaded.
Le Coq Manuel
Frequent Advisor

Re: C7000 Flex 10 virtual connect fiber channel

Problem is that even the OS loaded it remains the same even with the OS loaded. And I have a blade that still has not logged in so I can not install ESXi because it does not see the LUN
Johan Guldmyr
Honored Contributor

Re: C7000 Flex 10 virtual connect fiber channel

Ah ok.

The port mapping on the blades how is that set up?
Le Coq Manuel
Frequent Advisor

Re: C7000 Flex 10 virtual connect fiber channel

Yes The configuration is identical on all slides
nijokj
Trusted Contributor

Re: C7000 Flex 10 virtual connect fiber channel

you can configure port mapping by login in to onborad adminstrator , and check the currect port mapping settigs. If any of the ports are not mapped to any of the bays you can start the new wizard to start the mapping the devices.
Le Coq Manuel
Frequent Advisor

Re: C7000 Flex 10 virtual connect fiber channel

Ports are mapped (see attachment). I even reboot my Virtual Connect fiber.
cjb_1
Trusted Contributor

Re: C7000 Flex 10 virtual connect fiber channel

If you can, try switching a working and non-working blade. If the fault follows the hardware it's likely to be an issue with the mezzanine on the blade. If not, then it's likely to be a zoning issue.
JKytsi
Honored Contributor

Re: C7000 Flex 10 virtual connect fiber channel

update firmwares =)
Remember to give Kudos to answers! (click the KUDOS star)

You can find me from Twitter @JKytsi
Johan Guldmyr
Honored Contributor

Re: C7000 Flex 10 virtual connect fiber channel

When you say that it is not working: what does that mean?

When you go into the FC HBA BIOS it doesn't see any LUNS or?

As always, are you running a good firmware set?
For example, are you running FOS 6.3.0x on the switches? (if they are brocade).