Hi All,

We are planning to buy HP blade servers (c7000) for that we need to plan for the power requirement for these servers.

Currently, In our lab we have more than 30 HP Rx2660 servers and they are consuming not more than 90A.

Could anyone please tell me how to plan for the power requirements of these servers and what is the maximum power requirement for 18 blade servers.

In addition to that, i also want to know should there be separate power supply for enclosures and servers??

I have lots of confusion in this regard, bcz i never worked on blade systems. I ll be grateful to you all for the help.

Thanks in advance,

Amit

5 REPLIES 5
Sameer_Nirmal
Honored Contributor

Re: Hp Blade c7000 Integrity servers power requirement!!

Enclosure power supply modules attached to enclosure provides power to blades and enclosure.

For power requirements, you may want to use
HP BladeSystem Power Sizer

http://h71019.www7.hp.com/ActiveAnswers/cache/347628-0-0-0-121.html


http://h18004.www1.hp.com/products/blades/components/c-class-tech-planning.html

Re: Hp Blade c7000 Integrity servers power requirement!!

Hi,

In the active answrsl link posted by Sameer you should put all features for the c7000, such as commucnication bays, and full features of your servers.

To connect the power subsystem of the blade encloshure system, view the configuration rules in the next document link

http://h20000.www2.hp.com/bc/docs/support/SupportManual/c00816246/c00816246.pdf

SoorajCleris
Honored Contributor

Re: Hp Blade c7000 Integrity servers power requirement!!

Hi Amit.

Could anyone please tell me how to plan for the power requirements of these servers and what is the maximum power requirement for 18 blade servers.

For C7000 you can insert 6 power supply modules. Each power supply will consume 2250W

If it is in N+N = 3+3 redundant mode.
Total = 6750 W

If you configure N+1 Mode = 11250W.

Regards,
Sooraj
"UNIX is basically a simple operating system, but you have to be a genius to understand the simplicity" - Dennis Ritchie
SoorajCleris
Honored Contributor

Re: Hp Blade c7000 Integrity servers power requirement!!

In addition to that, i also want to know should there be separate power supply for enclosures and servers??

No. The servers are inserted in enclosures (ofcourse). So you will give power to the enclosure.
"UNIX is basically a simple operating system, but you have to be a genius to understand the simplicity" - Dennis Ritchie
astra
Frequent Advisor

Re: Hp Blade c7000 Integrity servers power requirement!!

Hi,

I used the power sizer tool and i got the report, and here i am little bit confused. Please someone can make me understand what all the parameters means??

Total System Leakage Current per Branch
0 Milliamp(s)

Total System Inrush Current per Branch (2 mS)
210 Amp(s)

Total System Weight (Includes Power and Rack)
684 Pounds(lbs) [310 Kilograms(kg)]

Input Voltage
240 Vac

c-Class Power Details

Power Credentials
Idle
Utilization
Circuit Sizing/HPTC
Unit(s)

Total Input Power
2925
3684
4113
Watt(s)

Total Input VA
2985
3760
4197
VA

BTU
9976
12564
14027
BTU(s)

Total Input Current
4.15
5.22
5.83
Amp(s)

Total Airflow in CFM
226
293
439


Total Airflow in CMM
6.413
8.301
12.424


Enclosure # 1 , 8 Fans , 6 PSU

Power Credentials
Idle
@ 100% Utilization
Circuit Sizing/HPTC
Unit(s)

Input Power
2925
3684
4113
Watt(s)

Input VA
2985
3760
4197
VA

BTU
9976
12564
14027
BTU(s)

Input Current
4.15
5.22
5.83
Amp(s)

Input Current Per Cord
2.073
2.611
2.915
Amp(s)

Airflow in CFM
226
293
439


Airflow in CMM
6.413
8.301
12.424




We have one enclosure and 6 full height blade servers, roughly what is the power requirement??