HPE Community read-only access December 15, 2018
This is a maintenance upgrade. You will be able to read articles and posts, but not post or reply.
Hours:
Dec 15, 4:00 am to 10:00 am UTC
Dec 14, 10:00 pm CST to Dec 15, 4:00 am CST
Dec 14, 8:00 pm PST to Dec 15, 2:00 am PST
BladeSystem - General
cancel
Showing results for 
Search instead for 
Did you mean: 

Take Power Supply Offline on c7000 to make a phase shift.

 
SOLVED
Go to solution
Jorgen Stenberg
Occasional Advisor

Take Power Supply Offline on c7000 to make a phase shift.

Due to problem with unbalanced phase load we have to reconfigure our c7000 enclosures regarding phase load. So my question is: Is it possible to take a power supply offline to make the phase shift. I presume that hot-plugging a power supply under load is not the best way of doing this. I would very much like an answer that´s not force me to make a complete power off on the entire enclosure to have this done.

/Jorgen
2 REPLIES
Raghuarch
Honored Contributor
Solution

Re: Take Power Supply Offline on c7000 to make a phase shift.

Access the OA.
Go to Power Management page.
Select Power Supply Redundant. Click Apply.

You can take a Power supply out with all the load. it doesn't bring down the enclosure.
as long as the remaining power supplies are present.
Jorgen Stenberg
Occasional Advisor

Re: Take Power Supply Offline on c7000 to make a phase shift.

Thanks for your answer. Phase shift is done without any blue lightnings so it was good answer.