Re: blade in critical off state

 
route
New Member

blade in critical off state

the blade had a green light but red x and the ilo wasnt able to communicate. so i did a server reset and now the blade is in a critical off state. any suggestions? thanks
7 REPLIES 7
marcus1234
Honored Contributor

Re: blade in critical off state

log in to the onboard admin

click on insight display keep burrowing in what does it say

also can you ping the ilo
what is in the iml log post it

also when in the onboard admin on left click on the left where it says rack firmware and post a screen shot

try the blade in another slot and another bladee in this one if poss..
as a quick fix try from cli command

reboot the oA

now what is the situation ??

have you made any changes lately
route
New Member

Re: blade in critical off state

thanks for the help.
i'll add the insight display info in a second post.

cannot ping iLo
what is iml log?
i have to make arrangements with data center help to move blade

try what from cli command?

I rebooted OA - still the same

no changes

screen shot attached
route
New Member

Re: blade in critical off state

so the insight display has a management processor failed error.

and then it talsk about firmware needing to be ilo2 1.30. I'm at ilo2 1.78.

reseating or restting may also help it says.

I'm trying to get someone out in the DC to reseat for me. just a matter of time now.
marcus1234
Honored Contributor

Re: blade in critical off state

ok iml log is a log in the ilo

but as you cannot ping it can you ping the nic

also try reseat the blade if it does not help

do this


clear nv ram

blade clear nvranm
Clearing the system configuration
To clear the system configuration:
1. Power down the server blade
2. Remove the server blade
3. Remove the access panellook at the diagram on it it will show the position of the maintenace switch( it clears Nv ram)
4. Change position 6 of the system maintenance switch to on.
5. Install the access panel
6. Install the server blade in the enclosure and power up the server blade.
7. Wait for the POST message that prompts you to change the switch setting:
Maintenance switch detected in the "On" position.
Power off the server and turn switch to the "Off" position.
8. Repeat steps 1 through 3.
9. Change position 6 of the system maintenance switch to off.
10. Repeat steps 5 through 7.


if that does not help try min config in the blade remove all disks , cards , and min ram ,
and down to one processor if needed eventually

if issue persists update the ilo from the front with directly connected console cable
if possible
keep posted so we can sort it

This is how we thank in the forum

http://forums11.itrc.hp.com/service/forums/helptips.do?#33



route
New Member

Re: blade in critical off state

the mother ended up being replaced
route
New Member

Re: blade in critical off state

the mother ended up being replaced
marcus1234
Honored Contributor