- Community Home
- >
- Servers and Operating Systems
- >
- HPE BladeSystem
- >
- BladeSystem - General
- >
- C7000 Intermitent Fan Fault
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
06-21-2018 07:07 AM
06-21-2018 07:07 AM
Hi,.
We have a c7000 with populated with 10 blades, OA version 4.70, and Virtual connect v4.50. About 6 weeks ago, the c7000 started alerting that the fan in slot 5 was faulty, we swapped the fan with the fan in another slot to confirm the fault moved with the fan. a replacement fan was then sent out by HPE support.
However the c7000 reported a few times per hour that the fan in slot 5 is removed, then it reports its absent, it reports fan is inserted and finally fan5 is OK. (those are email alerts which arrive all within 10 seconds) If i have the OA console open, i see the status of fan 5 briefly flash from present to removed to inserted. Between these events the fan is showing as operating normally, and the light on the back of the fan remains green.
With HPE support we have tried upgrading the OA to 4.80, then back down. We have removed and re-inserted the OA's and OA tray. We have also replaced the OA tray and the active OA, but we are still getting the email alerts from the OA several times per hour.
HPE advise next course of action is to replace the backplane in the c7000, but as that causes significant downtime for the c7000 does anyone have any other thoughts on the cause/resolution ?
Thanks.
Steve
Solved! Go to Solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
06-22-2018 05:07 AM
06-22-2018 05:07 AM
SolutionAfter a searching for solutions, i saw this article
https://support.hpe.com/hpsc/doc/public/display?docId=mmr_kc-0115448
and all out fans had been at 89%, and from memory probably like that for years.
Not sure what triggered the alerts to start last month, but soon as i changed the thermal cooling to optimal the alerts all stopped, and physical fans dropped to a much lower speed.
ok,
Steve