BladeSystem Server Blades
cancel
Showing results for 
Search instead for 
Did you mean: 

ProLiant BL465c G7 PSP 8.60.0.0 Erroneous SNMP Trap 3033_4

 
Donald J Wood
Frequent Advisor

ProLiant BL465c G7 PSP 8.60.0.0 Erroneous SNMP Trap 3033_4

Last night someone reported that the server trapped with a 3033_4. I was able to verify this in our alerting log in our alerting system.

 

I know that the 3033_4 is a cable issue and it's source is the Intelligent Drive Array Controller. The CPQIDA-MIB DEFINITIONS is the source MIB file.

 

Server is running W2k8 R2 Enterprise. The system managmenet home page doesn't show any errors, the IML hasn't logged an event in 4 months, and the windows system event logs have no such event. I checked our alerting system and it's fine. The source ip address informaiton of the alert matches the ip address assigned to the HOST that supposed to have alerted. I even pinged the server from the alert server console and the name resolves correctly.

 

Here's the trap informaiton.

serverhostname, 16, Slot 0, 4, 3, 39, 5001438011FD8160, 5.70, 1048576

 

[1.3.6.1.2.1.1.5.0, 1.3.6.1.4.1.232.11.2.11.1.0, 1.3.6.1.4.1.232.3.2.2.1.1.20.4, 1.3.6.1.4.1.232.3.2.2.1.1.1.4, 1.3.6.1.4.1.232.3.2.2.1.1.10.4, 1.3.6.1.4.1.232.3.2.2.1.1.2.4, 1.3.6.1.4.1.232.3.2.2.1.1.15.4, 1.3.6.1.4.1.232.3.2.2.1.1.3.4, 1.3.6.1.4.1.232.3.2.2.2.1.12.4]

 

I'm going to have our operations group reboot the HOST and watch the POST in the ILO to see if it produces a POST error message.

1 REPLY 1
Matti_Kurkela
Honored Contributor

Re: ProLiant BL465c G7 PSP 8.60.0.0 Erroneous SNMP Trap 3033_4

The trap 3033 is cpqDa6CntrlStatusChange:

Controller Status Change.

This trap signifies that the agent has detected a change in
the status of a drive array controller.  The variable
cpqDaCntlrBoardStatus indicates the current controller status.

User Action: If the board status is generalFailure(3), you
may need to replace the controller.  If the board status is
cableProblem(4), check the cable connections between the
controller and the storage system.

Contained in Module(s):
CPQIDA-MIB

 

The trap information objects are, in order:

  • sysName (= serverhostname)
  • cpqHoTrapFlags (= 16, see below)
  • cpqDaCntrlHwLocation (= Slot 0)
  • cpqDaCntrlIndex (= 4)
  • cpqDaCntrlBoardStatus (= 3 = generalFailure)
  • cpqDaCntrlModel (= 39 = sa-p410i)
  • cpqDaCntrlSerialNumber (= 5001438011FD8160)
  • cpqDaCntrlFWRev (= 5.70)
  • cpqDaAccelTotalMemory (= 1048576)

So it does not look like a cable problem (status 4), but a general failure (status 3) in controller #4 (which is Slot 0 as indicated).

 

 

The description of the cpqHoTrapFlags in the MIB file is as follows:

This is a collection of flags used during trap delivery.
Each bit has the following meaning:

Bit 5-31: RESERVED: Always 0.
Bit 2-4: Trap Condition
0 = Not used (for backward compatibility)
1 = Condition unknown or N/A
2 = Condition ok
3 = Condition degraded
4 = Condition failed
5-7 = reserved
Bit 1:    Client IP address type
0 = static entry
1 = DHCP entry
Bit 0:    Agent Type
0 = Server
1 = Client

NOTE:   bit 31 is the most significant bit, bit 0 is the least
significant.

Contained in Module(s):
CPQHOST-MIB

 Value 16 is 0x00000010 in hex, so only bit 4 is set. So the value of bits 2-4 is 4: that's "Condition failed". 

 

Before rebooting, you might use the ACU to verify the state of the disk array controller(s).

 

The current firmware version for Smart Array P410i is 9.30, so your version 5.70 seems very, very old. While you're at the ACU, verify the firmware version and consider updating if necessary.

MK