BladeSystem - General
1753808 Members
7794 Online
108805 Solutions
New Discussion юеВ

Re: 650FLB with a HP VC Flex-10 Enet Module

 
JoegSandia
Occasional Contributor

650FLB with a HP VC Flex-10 Enet Module

Hi Community,

So, we have a C7000 enclosure with a HP VC Flex-10 Enet Module and a 10g uplink. In our Gen9's, we have a 650FLB with latest firmware on all devices (Well, the VC modules are 4.31) and we cannot get the OS to see the network...

OS is ESXi 5.5.0 U3.

After taking a look at the specs on the card and the VC module, its possible that the 20/40 card is not compatible with the VC module. There are some documents that say it is, and others that dont.

Can someone verify that this card and VC module will work together? Just want to rule this out before we do any more network troubleshooting.

Thanks!
Joe

3 REPLIES 3
msh_it
Regular Advisor

Re: 650FLB with a HP VC Flex-10 Enet Module

Hi Joe

As per the card quick spec, it should support VC Flex-10, so I dont belive this is your problem

Card quick spec http://www8.hp.com/h20195/v2/GetPDF.aspx/c04347341.pdf

 

-------------------------------

msh_it | UAE | AbuDhabi

If you feel this was helpful please click the KUDOS! Below!
JoegSandia
Occasional Contributor

Re: 650FLB with a HP VC Flex-10 Enet Module

Hi msh_it,

Thanks for the reply! You are correct, and the issue was a VCM firmware revision. The VMC we had in prodution was old so we updated it to the newest version and its working now. Sorry I didnt update the post when we did that.

Thanks again for the reply!
Joe

JoegSandia
Occasional Contributor

Re: 650FLB with a HP VC Flex-10 Enet Module

HAH, so many issues we have been working on lately... The VC Firmware was for another issue...

This issue was an upstream network VLan issue...

Sorry for the mistake :).

Joe