If I connect a VA7400 to a UPS, do I need to change any of the configuration of the VA7400 so that it is aware of the UPS and uses it when a power interrupt occurs?

Kurt
1 REPLY 1
Enes Dizdarevic
Honored Contributor

Re: VA7400 - UPS

VA box is not "UPS aware" so you can not automatically change its status based on UPS messsages. What you can do is to connect server with commandview to the same UPS and include commandview commands in server based UPS scripts. In this scripts you can for example change VA caching mode (set resiliency level), or shutdown VA before shuting down server, etc.