Hi,

After installing any disk on any enclosure I get the following issue. The currnt firmware version is XCS 6.110.

May I follow this process on-line?

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?objectID=c01914371&dimid=1006920700&dicid=alr_oct09&jumpid=em_alerts/us/oct09/all/xbu/emailsubid/mrm/mcc/loc/rbu_category/alerts

Thanks.
Best regards,
Javier.
2 REPLIES 2

Re: EVA 8000 HSV210 controller error after install disk

Sorry, I forgot the issue:

The HSV210 controller has detected an enclosure on the Fibre Channel but is unable to communicate with the Drive Enclosure Environmental Monitoring Unit on the enclosure address bus or the Drive Enclosure Environmental Monitoring Unit is reporting an invalid enclosure number.
View corrective actionsCorrective action code: c5

Thanks.
Javier.
V├нctor Cesp├│n
Honored Contributor
Solution

Re: EVA 8000 HSV210 controller error after install disk

These events appear when there's any disturbance on the loops. For example when you add a disk or when a disk is causing packet loss.

The traffic to the EMUs has low priority and gets delayed. That's what those events are about. All packets are resent if they do not arrive on the expected time, so this has no consequences.