- Community Home
- >
- Servers and Operating Systems
- >
- Operating Systems
- >
- Operating System - HP-UX
- >
- Integrity server ready before MSA1500
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 10:15 AM
тАО02-19-2009 10:15 AM
The problem is that at bootup, the server outruns the MSA. This results in the server not seeing the MSA LUNs via the bootup sequence.
It's easily fixed by doing an ioscan, and a vgchange. But, I'd like to figure a way to have this done during the boot process.
Thoughts? Someone else has to have run into this also.
Solved! Go to Solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 10:53 AM
тАО02-19-2009 10:53 AM
Re: Integrity server ready before MSA1500
power up the switch, the msa and finally the server(s).
I guess you will not do this every morning ...
;-))
Hope this helps!
Regards
Torsten.
__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.
__________________________________________________
No support by private messages. Please ask the forum!
If you feel this was helpful please click the KUDOS! thumb below!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 11:16 AM
тАО02-19-2009 11:16 AM
Re: Integrity server ready before MSA1500
When the power is restored, both the server and the MSA1500 are powered up. The problem is that the MSA takes longer to get itself in order than the server does. Result is missing LUNs.
As this is at a remote site, we end up with a phone call that their application isn't working.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 11:24 AM
тАО02-19-2009 11:24 AM
Re: Integrity server ready before MSA1500
The only safe workaround is a manual power on in a proper sequence IMHO ...
Hope this helps!
Regards
Torsten.
__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.
__________________________________________________
No support by private messages. Please ask the forum!
If you feel this was helpful please click the KUDOS! thumb below!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 11:30 AM
тАО02-19-2009 11:30 AM
Re: Integrity server ready before MSA1500
wing order:
1. Storage Enclosures├в Power on all storage expansion enclosures.
2. MSA1500 cs├в Power the MSA1500 cs on with the power switch located in the far-right
lower area of the front panel. After powering on, wait until the message ├в MSA1000
Startup Complete├в appears on your display. This process may take up to two
minutes.
3. Server(s)├в Ensure that the servers that are attached to the MSA1500 cs are powered on.
Hope this helps!
Regards
Torsten.
__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.
__________________________________________________
No support by private messages. Please ask the forum!
If you feel this was helpful please click the KUDOS! thumb below!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 11:33 AM
тАО02-19-2009 11:33 AM
Re: Integrity server ready before MSA1500
Applying power
Before applying power to the MSA1500 cs all components of the storage system must be
installed and connected to the supported interconnect options
The MSA1500 cs components must be powered up in the following order:
1. Storage Enclosures Power on all storage expansion enclosures.
2. MSA1500 cs Power the MSA1500 cs on with the power switch located in the far-right
lower area of the front panel. After powering on, wait until the message ├в MSA1000
Startup Complete├в appears on your display. This process may take up to two
minutes.
3. Server(s)├в Ensure that the servers that are attached to the MSA1500 cs are powered on.
Hope this helps!
Regards
Torsten.
__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.
__________________________________________________
No support by private messages. Please ask the forum!
If you feel this was helpful please click the KUDOS! thumb below!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 11:41 AM
тАО02-19-2009 11:41 AM
Re: Integrity server ready before MSA1500
This is really much less complex that it appears.
The MSA-1500 must start first and be fully spun up before the server start sequence begins.
You can do this by providing it a different UPS to give it a better chance of running through the power failure.
APC sells PDU Power Distribution Units that can permit you to program delays in the startup sequence plug by plug, permitting you to control the startup sequence.
You could also make an /sbin/init.d start up job and position it at the beginning of run level 2 to slow down the server startup. Problem with that approach is that when you are patching you will find the delay maddening.
If you are getting power outages frequently enough for this to be a problem, you need to talk to management about a server room UPS that can ride your critical servers through a long outage.
SEP
Owner of ISN Corporation
http://isnamerica.com
http://hpuxconsulting.com
Sponsor: http://hpux.ws
Twitter: http://twitter.com/hpuxlinux
Founder http://newdatacloud.com
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 12:52 PM
тАО02-19-2009 12:52 PM
Re: Integrity server ready before MSA1500
So, I'm going to add a script into /sbin/init.d.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 04:32 PM
тАО02-19-2009 04:32 PM
Re: Integrity server ready before MSA1500
Yes, myself, I use a careful power up sequence in my kitchen, and for my entertainment system, and for my basemetn coputer lab, and for my car. Like I'll switch on the lights in the car _after_ I cold start the car to avoid the extra 15 amps drain on the battery. My kids have a 4 letter word for that. It stars with an a and ends in "an l".
I find it entirely unreasonable to have to power up a system in some particular careful order. (but do it anyway).
If order is needed, then it should be imposed through automation not by a playbook.
It should be possible to loose all power, and
bring it all back un-attended with the flip of one switch (the power company).
The init.d script should be there to check that the resources are in place to move to a next level in the init. If I have drives... mount then and onwards... otherwise write message, wait and try again. If I have a network, then onwards, ... otherwise write a message (where? :-), wait and try again. If I can bring up Oracle then onwards else .. page someone.
fwiw,
Hein
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-19-2009 04:50 PM
тАО02-19-2009 04:50 PM
Solution