- Community Home
- >
- Servers and Operating Systems
- >
- Legacy
- >
- HPE 9000 and HPE e3000 Servers
- >
- Re: Minimum to keep rp7420 running
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2011 08:26 AM
тАО02-01-2011 08:26 AM
We have a rp7420 with two partitions. In each partition, a cell is running.
Due to we have some electrical issues, we want to reorder the electrical cables in the data center.
As the services on the rp7420 are critical, we don't want shutdown the server.
I know that the server have four entries for power cords (A0, A1, B0, B1) and two BPS (BPS0 and BPS1).
My questions are:
How many power cords are the minimum necessary to keep the server running ?
With MP, How could I verify the operational state of the power cords (A0, A1, B0, B1) ?
Thanks in advance
Solved! Go to Solution.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2011 08:58 AM
тАО02-01-2011 08:58 AM
SolutionThe minimum necessary is one of them, others are redundant to avoid power outages. In your case if have four power cords (A0, A1, B0 and B1) can distribute them enter your couple power sources (BPS0 and BPS1). This mean A0 & B0 in BPS0, and A1 & B1 in BPS1. Of course, I guess that BPS0 and BPS1 are differents power nets. This not only will guard you in case of electrical outages, also offers you done electrical maintenance at invidual nets without disturb your system production.
HP-UX have the Event Monitoring Service (EMS) daemon to detect any hardware failure, including power sources (A0, A1, B0 and B1). Event notification ussually makes by /var/adm/syslog/syslog.log file. You could analyze the content of this file, or configures other notification ways (i.e:email message).
AT MP layer you could consult the hardware events log.
Rgds.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2011 09:06 AM
тАО02-01-2011 09:06 AM
Re: Minimum to keep rp7420 running
rp7420 is a cell based server. Each cell has electrical isolation.
Technically you can run the complex on a single plug to the power supply that runs the cell. This might result in you finding a power supply that is flaky and some downtime anyway.
At the very least your user community needs to be warned of potential downtime. Better still to actually schedule some.
nparstatus will provide you some information as will the console based utilities.
SEP
Owner of ISN Corporation
http://isnamerica.com
http://hpuxconsulting.com
Sponsor: http://hpux.ws
Twitter: http://twitter.com/hpuxlinux
Founder http://newdatacloud.com
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2011 10:36 AM
тАО02-01-2011 10:36 AM
Re: Minimum to keep rp7420 running
Favourite Toy:
AMD Athlon II X6 1090T 6-core, 16GB RAM, 12TB ZFS RAIDZ-2 Storage. Linux Centos 5.6 running KVM Hypervisor. Virtual Machines: Ubuntu, Mint, Solaris 10, Windows 7 Professional, Windows XP Pro, Windows Server 2008R2, DOS 6.22, OpenFiler
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2011 12:39 PM
тАО02-01-2011 12:39 PM
Re: Minimum to keep rp7420 running
To give you a precise technical information about this theme, please refer at this HP-9000 rp7420 Server document. AC/DC Power section:
http://h18000.www1.hp.com/products/quickspecs/11895_div/11895_div.HTML#Configuration
The service processor (MP or GSP) has a set of menus that give you access to various commands, consoles, log files, and other features. The Command-Menu includes service, status, system access, and other
commands:
GSP:CM>PS
PS=Display detailed power and hardware configuration status.
I hope to have resolved on this occasion your questions.