re : rp3440 problem

 
SOLVED
Go to solution
Vincent_5
Super Advisor

re : rp3440 problem

Hi Guys,
Can anyone help, can I know if the RP3440 can automatically shutdown when it detect the environment temperature is over heating , is there any document that have a write out that there is such a feature.

Please advice??

Regards
Vincent
nothing is better than to know more
4 REPLIES 4
Torsten.
Acclaimed Contributor
Solution

Re: re : rp3440 problem

Yes, this server will do the following if temperature is getting higher:

- warning
- critical warning
- shutdown
- power off

Hope this helps!
Regards
Torsten.

__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.

__________________________________________________
No support by private messages. Please ask the forum!

If you feel this was helpful please click the KUDOS! thumb below!   
Vincent_5
Super Advisor

Re: re : rp3440 problem

Hi Torsen,
Thanks for the info.

Regards
Vincent
nothing is better than to know more
Andrew Rutter
Honored Contributor

Re: re : rp3440 problem

hi,

yes the server will automatically shutdown if over temp, you should get notifications first with the ems running

in the site prep guide it states this

Over-temperature shutdown +40├В┬░C (+104├В┬░F)

http://docs.hp.com/en/A7137-96005/A7137-96005_rp3410_rp3440_Siteprep.pdf

Andy
Bill Hassell
Honored Contributor

Re: re : rp3440 problem

While the HP server will shutdown in case of over temperature, don't forget that all your tape drives, disk drives, and network equipment will probably not shutdown and therefore will be damaged by high temperatures. A typical data center that loses air conditioning will rise to very high levels (130 F to 160 F). At that level, most of you equipment (except the rp3440) is permanently ruined and must be replaced.

I would always design a data center with an emergency overtemp sensor for the entire room. Once the maximum temperature is reached (typically 100 F to 110 F) then all power is removed from the center. The equipment is far too expensive to risk damage from a bad air conditioner.


Bill Hassell, sysadmin