what would happen when one VRM failed on CELL of rp7420?

 
SOLVED
Go to solution
stephen peng
Valued Contributor

what would happen when one VRM failed on CELL of rp7420?

guys,
check the attachment.
there are 15 VRMs on CELL 0 of this rp7420, now VRM #2 "VOLTAGE FAULT",
1, what would happen if I don't replace this failed VRM?
2, what function each VRM on this CELL serves?
3, would there be VRM at HP parts store?
4, what those "1"s above "VRM's" stand for?
1 1 1 1 1 1

VRM's 1 2 3 4 5 6 7 8 9 0 1 2 3 4 5

regards
Stephen
5 REPLIES 5
Torsten.
Acclaimed Contributor

Re: what would happen when one VRM failed on CELL of rp7420?

Without having any documentation in front of me I can tell you this:

1) something will not work
2) They delivery different voltages to the cell components
3) check partsurfer.hp.com , some VRMs are FRUs
4) this is 10, 11 , ... 15 (read from top)

Hope this helps!
Regards
Torsten.

__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.

__________________________________________________
No support by private messages. Please ask the forum!

If you feel this was helpful please click the KUDOS! thumb below!   
stephen peng
Valued Contributor

Re: what would happen when one VRM failed on CELL of rp7420?

Is this VRM #2 a high voltage or a low one?

regards
Stephen
hvhari
Esteemed Contributor

Re: what would happen when one VRM failed on CELL of rp7420?

It is a low voltage VRM "Power status : on, 1.2V Module 1, VRM #2 VOLTAGE FAULT"

Regards,
Hari

If this post was useful , click the Kudos Star on the left side to say Thanks!
Robert_Jewell
Honored Contributor
Solution

Re: what would happen when one VRM failed on CELL of rp7420?

VRM 2 serves the power rail supporting the CPU's. You only have two CPU's installed, so perhaps this is why you have not seen any problems.

HP's part # for this VRM is 0950-4122 or 0950-4708. However, there is a warning to be aware of. All of the low voltage VRMs should be of the same manufacturer. So, when you replace the part check to be sure else the cell power rails may become unstable.

If you can, contact HP Support for help on this if needed.

-Bob
----------------
Was this helpful? Like this post by giving me a thumbs up below!
stephen peng
Valued Contributor

Re: what would happen when one VRM failed on CELL of rp7420?

yes, I know that there are two kind of low voltage VRM.