Chung, jin-won
New Member

Re: OVERTEMP_EMERG WARNING

hi there.

condition of temperature is

i) overtemp_normal : normal
ii) overtemp_crit : above 30 degree celcius
iii) overtemp_emerg : above 35 degree celcius

there's also configuration file in /etc/envd.conf
you can see action script like following text


OVERTEMP_CRIT:y

OVERTEMP_EMERG:y
/usr/sbin/reboot -qh

FANFAIL_CRIT:y

FANFAIL_EMERG:y
/usr/sbin/reboot -qh
Carlos Munoz Lopez
Frequent Advisor

Re: OVERTEMP_EMERG WARNING

Thank you all guys!!! Thanks for all your support. I solved the problem, in fact, as you suggested, there was a problem with one of the fans which wasn't working properly. I called HP tech support and they notified me there was a problem with all of the rp24xx server. It was a factory tech failure that was responsible for an over temperature state which could result in system shut down. The problem was solved adding a missing part (A6889-62005). Once this part was installed, the temperature state returned to normal. Thank you!!!