- Community Home
- >
- Servers and Operating Systems
- >
- Legacy
- >
- HPE 9000 and HPE e3000 Servers
- >
- Re: PDU required for rp5470 200v?
HPE 9000 and HPE e3000 Servers
1748163
Members
3639
Online
108758
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-01-2004 02:11 PM
тАО02-01-2004 02:11 PM
PDU required for rp5470 200v?
Hi,
The machine was installed in a standard (non-HP) 19" rack and we opted to use the rack's 100v power strips to supply the N+1. Now the rack has been filled with other higher priority machines and we have been told to use a separate 200v circuit for the rp5470 instead. HP tells me the only option is to install a PDU, but there's no space. I want to connect C-13-to-L6-20 cables ( like at http://www.internationalconfig.com/icc6.asp?item=93900 ) between all three power supplies and UPS-backed L6-20 receptacles under the floor. Is there any reason I shouldn't do this?
Thanks,
Jon
The machine was installed in a standard (non-HP) 19" rack and we opted to use the rack's 100v power strips to supply the N+1. Now the rack has been filled with other higher priority machines and we have been told to use a separate 200v circuit for the rp5470 instead. HP tells me the only option is to install a PDU, but there's no space. I want to connect C-13-to-L6-20 cables ( like at http://www.internationalconfig.com/icc6.asp?item=93900 ) between all three power supplies and UPS-backed L6-20 receptacles under the floor. Is there any reason I shouldn't do this?
Thanks,
Jon
3 REPLIES 3
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-03-2004 04:12 AM
тАО02-03-2004 04:12 AM
Re: PDU required for rp5470 200v?
The current that you rp5470 will draw across all three power supplies is 6.5 Amps at 200V. Therefore, if you plug into three separate circuits you are not using much of each 20 amp circuit. If you don't use separate circuits then the circuit becomes a single point of failure (might or might not be acceptable). If you are using an E-series rack then there are several PDU option including some that don't take any U of space because they are on the side. The problem is that you would need three or you are back to using a single circuit. More info on options at www.hp.com/racksolutions, a.k.a. http://h30140.www3.hp.com/
Mom 6
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-03-2004 04:04 PM
тАО02-03-2004 04:04 PM
Re: PDU required for rp5470 200v?
Ted,
Thanks. Actually I need to know if there's any reason I should _not_ connect 250v rated cables directly from my server to my available power sources (they would be C-15-to-L620).
Regards,
Jon
Thanks. Actually I need to know if there's any reason I should _not_ connect 250v rated cables directly from my server to my available power sources (they would be C-15-to-L620).
Regards,
Jon
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-04-2004 09:20 AM
тАО02-04-2004 09:20 AM
Re: PDU required for rp5470 200v?
There's no reason not to. I have used servers in that configuration many times. All of HP's more recent servers have automatic voltage sensing built in.
Josh
Josh