UPS 3000VA

 
Vandewiele_1
Occasional Visitor

UPS 3000VA

Hi,

i'm trying to connect a UPS 3000VA serial number E00111365 acquires in 98 to a win 2000 or 2003 server. But the server can't recognize it ? aren't the old ups not supported by win 2000 or 2003. In fact, I would like to check the ups with HPPM because a red led under the battery picture is always flashing. I've the same problem with an other older 1500 VA ups

Thanks for your help
2 REPLIES 2
Thierry Poels_1
Honored Contributor

Re: UPS 3000VA

hi,

concerning the red led....
the battery of the UPS might be dead (batteries tend to have a limited lifetime).
Did you try to connect a PC or something else to the UPS, and then remove power from the UPS? Did it drop dead or keeps on running?

regards,
Thierry.
All unix flavours are exactly the same . . . . . . . . . . for end users anyway.
Vandewiele_1
Occasional Visitor

Re: UPS 3000VA

thanks,

indeed I think it has to do with its lifetime, I tried to connect it to 2 differents servers ( win 2000 & win 2003 )but without success. when I remove the outlet the ups give us power for moreless 10 min. I found this "SNMP/Serial Port Card Compatibility With UPS R12000 XR And HP Rack And Power Manager " on hp site , perhaps linked ??

best regards

phil