Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

 
ElkabelNew
Occasional Advisor

Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

Hi guys,

I have got the same problem from 2 - 3 days with my Onbord Administrator (OA).

It's happened twice morning, when I come to work in our server room is too noisily. When I login in OA I seeing my blade servers with Critical errors : Management Processor :  Error - lost communication with ILO , and their fans spins on 98%.

The reboot it is not decision, but when I pull out OA module from the chassis and back it again, everything is OK

That from below is OA System Logs from when I have problem with my OA:

Aug 17 04:07:54 OA: Management Processor on Blade 1 appears unresponsive.
Aug 17 04:08:04 OA: Management Processor on Blade 2 appears unresponsive.
Aug 17 04:08:14 OA: Management Processor on Blade 3 appears unresponsive.
Aug 17 07:38:28 OA: Authentication failure for user admin from 192.168.11.203, requesting web service
Aug 17 07:38:46 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 17 08:29:45 OA: Blade removed from bay 3
Aug 17 08:29:45 OA: Blade inserted in bay 3
Aug 17 08:29:45 OA: Blade in bay #3 status changed to OK
Aug 17 08:29:45 OA: Management Processor on Blade 3 appears unresponsive.
Aug 17 08:31:45 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 08:33:45 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 08:44:19 OA: Blade removed from bay 3
Aug 17 08:44:19 OA: Blade inserted in bay 3
Aug 17 08:44:19 OA: Blade in bay #3 status changed to OK
Aug 17 08:46:19 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 08:47:37 OA: Management Processor on Blade 3 appears unresponsive.
Aug 17 08:48:19 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 09:31:39 OA: Blade removed from bay 3
Aug 17 09:31:40 OA: Blade inserted in bay 4
Aug 17 09:31:40 OA: Blade in bay #4 status changed to OK
Aug 17 09:33:40 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 09:35:04 OA: Management Processor on Blade 4 appears unresponsive.
Aug 17 09:35:40 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 09:44:11 OA: Blade removed from bay 4
Aug 17 09:44:11 OA: Blade inserted in bay 4
Aug 17 09:44:11 OA: Blade in bay #4 status changed to OK
Aug 17 09:46:11 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 09:47:35 OA: Management Processor on Blade 4 appears unresponsive.
Aug 17 09:48:11 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 10:37:36 OA: PowerDelay server settings have been changed.
Aug 17 10:39:57 OA: Blade removed from bay 4
Aug 17 10:39:57 OA: Blade inserted in bay 4
Aug 17 10:39:57 OA: Blade in bay #4 status changed to OK
Aug 17 10:41:58 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 10:43:21 OA: Management Processor on Blade 4 appears unresponsive.
Aug 17 10:43:58 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 10:44:54 OA: PowerDelay server settings have been changed.
Aug 17 10:57:36 OA: Onboard Administrator is rebooting
Aug 17 10:58:16 Kernel: Network link is up at 100Mbps - Full Duplex
Aug 17 10:58:17 OA: Time zone changed to GMT+2
Aug 17 10:58:19 OA: LCD Status is: OK.
Aug 17 10:58:21 Enclosure-Link: Service started
Aug 17 10:58:22 OA: Onboard Administrator booted successfully
Aug 17 10:58:31 Enclosure-Link: Initial topology scan completed successfully
Aug 17 10:59:48 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 17 11:00:32 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 11:01:24 OA: Management Processor on Blade 1 appears unresponsive.
Aug 17 11:01:30 OA: Management Processor on Blade 2 appears unresponsive.
Aug 17 11:01:42 OA: Management Processor on Blade 4 appears unresponsive.
Aug 17 11:02:56 OA: Blade removed from bay 4
Aug 17 11:03:13 OA: Blade inserted in bay 3
Aug 17 11:03:13 OA: Blade in bay #3 status changed to OK
Aug 17 11:04:56 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 11:06:31 OA: Management Processor on Blade 3 appears unresponsive.
Aug 17 11:06:56 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 11:12:51 Kernel: Network link is up at 100Mbps - Full Duplex
Aug 17 11:12:53 OA: Time zone changed to GMT+2
Aug 17 11:12:54 OA: Server Power Reduction Mode - Enabled
Aug 17 11:12:55 OA: LCD Status is: OK.
Aug 17 11:12:56 Enclosure-Link: Service started
Aug 17 11:12:58 OA: Onboard Administrator booted successfully
Aug 17 11:13:06 Enclosure-Link: Could not acquire bottom enclosure's UUID. Cannot set RUID.
Aug 17 11:13:06 Enclosure-Link: Initial topology scan completed successfully
Aug 17 11:13:08 OA: Blade 3 is reporting nominal health status.
Aug 17 11:13:08 OA: Blade in bay #3 status changed to OK
Aug 17 11:13:13 Enclosure-Link: RUID recovered: 09CZC9027XJ3
Aug 17 11:13:28 OA: Blade 1 is reporting nominal health status.
Aug 17 11:13:28 OA: Blade in bay #1 status changed to OK
Aug 17 11:13:32 OA: Blade 2 is reporting nominal health status.
Aug 17 11:13:32 OA: Blade in bay #2 status changed to OK
Aug 17 11:13:36 OA: Server Power Reduction - Deactivated
Aug 17 11:13:36 OA: Server Power Reduction Mode - Disabled
Aug 17 11:13:40 OA: Server blade in bay 3 has been powered on
Aug 17 11:13:40 OA: Blade 3 is properly cooled.
Aug 17 11:14:09 OA: Blade in bay #3 status changed to OK
Aug 17 11:14:25 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 17 11:14:29 OA: Blade in bay #1 status changed to OK
Aug 17 11:14:33 OA: Blade in bay #2 status changed to OK
Aug 17 11:15:08 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 11:15:08 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 17 11:17:08 Alertmail: Failed to send AlertMail to kiro@elkabel.bg

Aug 18 15:35:48 Kernel: Network packet flooding detected.
Aug 18 15:35:50 Kernel: Network packet flooding detected.
Aug 18 15:35:55 Kernel: Network packet flooding detected.
Aug 18 15:36:02 Kernel: Network packet flooding detected.
Aug 18 20:28:34 OA: Management Processor on Blade 1 appears unresponsive.
Aug 18 20:28:44 OA: Management Processor on Blade 2 appears unresponsive.
Aug 18 20:28:54 OA: Management Processor on Blade 3 appears unresponsive.
Aug 19 07:43:16 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 19 07:51:20 OA: Onboard Administrator is rebooting
Aug 19 07:52:00 Kernel: Network link is up at 100Mbps - Full Duplex
Aug 19 07:52:00 OA: Time zone changed to GMT+2
Aug 19 07:52:01 OA: LCD Status is: OK.
Aug 19 07:52:03 Enclosure-Link: Service started
Aug 19 07:52:04 OA: Onboard Administrator booted successfully
Aug 19 07:52:13 Enclosure-Link: Initial topology scan completed successfully
Aug 19 07:53:13 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 19 07:54:14 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 19 07:55:07 OA: Management Processor on Blade 1 appears unresponsive.
Aug 19 07:55:13 OA: Management Processor on Blade 2 appears unresponsive.
Aug 19 07:55:19 OA: Management Processor on Blade 3 appears unresponsive.
Aug 19 08:15:31 Kernel: Network link is up at 100Mbps - Full Duplex
Aug 19 08:15:32 OA: Time zone changed to GMT+2
Aug 19 08:15:34 OA: Server Power Reduction Mode - Enabled
Aug 19 08:15:36 OA: LCD Status is: OK.
Aug 19 08:15:38 Enclosure-Link: Service started
Aug 19 08:15:41 OA: Onboard Administrator booted successfully
Aug 19 08:15:47 Enclosure-Link: Initial topology scan completed successfully
Aug 19 08:15:47 OA: admin logged into the Onboard Administrator from 192.168.11.203
Aug 19 08:16:10 OA: Blade 1 is reporting nominal health status.
Aug 19 08:16:10 OA: Blade in bay #1 status changed to OK
Aug 19 08:16:15 OA: Blade 2 is reporting nominal health status.
Aug 19 08:16:15 OA: Blade in bay #2 status changed to OK
Aug 19 08:16:16 OA: Server Power Reduction - Deactivated
Aug 19 08:16:16 OA: Server Power Reduction Mode - Disabled
Aug 19 08:16:20 OA: Blade 3 is reporting nominal health status.
Aug 19 08:16:20 OA: Blade in bay #3 status changed to OK
Aug 19 08:17:10 OA: Blade in bay #1 status changed to OK
Aug 19 08:17:15 OA: Blade in bay #2 status changed to OK
Aug 19 08:17:20 OA: Blade in bay #3 status changed to OK

Aug 19 08:17:48 Alertmail: Failed to send AlertMail to kiro@elkabel.bg
Aug 19 08:18:08 Alertmail: Failed to send AlertMail to kiro@elkabel.bg

If someone has experience with similar errors please let me share what have to done.

Thank you in advance

6 REPLIES 6
Torsten.
Acclaimed Contributor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

Onbord Administrator 2.31 ???

The oldest version I still have on my disk is 2.60 from early year 2010.

Now we are at version 4.50.

 

Same age for ILO and BIOS?

 

So you probably missed 1000+1 fixes ...


Hope this helps!
Regards
Torsten.

__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.

__________________________________________________
No support by private messages. Please ask the forum!

If you feel this was helpful please click the KUDOS! thumb below!   
ElkabelNew
Occasional Advisor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

Hi,

My blade system ILO2:

Model iLO2 Firmware Version 1.61 Aug 31 2008 ROM Version I15 11/02/2008

 

OA:

Device Name BladeSystem c3000 Onboard Administrator Manufacturer HP Firmware Version 2.31 Hardware Version 0J

ElkabelNew
Occasional Advisor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

Is it problem on firmware versions !?

Torsten.
Acclaimed Contributor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

>>

My blade system ILO2:

Model iLO2 Firmware Version 1.61 Aug 31 2008 ROM Version I15 11/02/2008

 

This is not helpful without knowing the blade model.

 

>> Is it problem on firmware versions !?

 

Maybe.

Here is the list of all OA updates and fixes, have a look.

(consider an update!)

http://h20566.www2.hpe.com/hpsc/swd/public/detail?sp4ts.oid=5177951&swItemId=MTX_28d9ee65d0a543b9a456b3b5a5&swEnvOid=4064#tab-history

 


Hope this helps!
Regards
Torsten.

__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.

__________________________________________________
No support by private messages. Please ask the forum!

If you feel this was helpful please click the KUDOS! thumb below!   
ElkabelNew
Occasional Advisor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

I saw this, but we have not HP support, and we afraid to execute these operations.

Who will assume a responsibility if happens something badly, unless we.

What will you advise me !?

ElkabelNew
Occasional Advisor

Re: Problem with OA - Onbord Administrator 2.31 , Enclosure info - BladeSystem c3000 ?

Separately, from where I can download new firmwares