- Community Home
- >
- Storage
- >
- Midrange and Enterprise Storage
- >
- HPE EVA Storage
- >
- Re: Cisco MDS PortChannel over long distances, var...
HPE EVA Storage
1753261
Members
5264
Online
108792
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-06-2010 12:10 PM
тАО09-06-2010 12:10 PM
Cisco MDS PortChannel over long distances, variation in cable length
When designing a new SAN connecting two datacentres over some distance the question came up if we could use multiple dark fibres to create a PortChannel (ISL trunk in Brocade-talk I guess).
The restrictions on a Brocade equivalent came to mind; I can't have too much variation in the cable length in each individual cable in a trunk.
However, I've been unable to find much if there are any such restrictions for Cisco MDS. I found something a bit vague in a marketing flyer for Cisco MDS where they pointed out that a "competing vendor" [duh] has this restriction whereas Cisco does not.
Poring through the manuals, so far no mention of this. I suppose if there weren't any restriction, it wouldn't be mentioned.
Any comments?
The restrictions on a Brocade equivalent came to mind; I can't have too much variation in the cable length in each individual cable in a trunk.
However, I've been unable to find much if there are any such restrictions for Cisco MDS. I found something a bit vague in a marketing flyer for Cisco MDS where they pointed out that a "competing vendor" [duh] has this restriction whereas Cisco does not.
Poring through the manuals, so far no mention of this. I suppose if there weren't any restriction, it wouldn't be mentioned.
Any comments?
2 REPLIES 2
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-27-2010 06:52 AM
тАО09-27-2010 06:52 AM
Re: Cisco MDS PortChannel over long distances, variation in cable length
Charles - did you get anywhere with this?
Am planning to set this up with my existing MDS9134's
HP, Cisco and EMC have assured me the configuration is supported but I can't find anyone who has actually set this up and can verify that its more than "airware".
Any feedback on your experience so for would be very welcome.
Am planning to set this up with my existing MDS9134's
HP, Cisco and EMC have assured me the configuration is supported but I can't find anyone who has actually set this up and can verify that its more than "airware".
Any feedback on your experience so for would be very welcome.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО09-28-2010 09:32 AM
тАО09-28-2010 09:32 AM
Re: Cisco MDS PortChannel over long distances, variation in cable length
I used two physical pairs of dark fibre, but I also installed a CWDM solution to split these two pairs into four connections. I connected each switch to both physical fibres, but logicially seperated on different wavelengths. Might sound confusing if you're unfamiliar with CWDM.
The net result was that I had two fabrics with two ISLs in each fabric, and they take two different paths per fabric. So far, I can get link OK, but I've not put any load on the connections yet.
The net result was that I had two fabrics with two ISLs in each fabric, and they take two different paths per fabric. So far, I can get link OK, but I've not put any load on the connections yet.