HPE EVA Storage
1751894 Members
5298 Online
108783 Solutions
New Discussion юеВ

Re: EVA4100 Battery status is holding charge

 
SOLVED
Go to solution
manuj kumar
Frequent Advisor

EVA4100 Battery status is holding charge

Hello All

I am facing a problem with the EVA4100 controller battery.
one of the second controller batteries status changed to "holding charge"
and a strange Led indication appeared

The Status led flashing green and then the Fault led flashing amber
yesterday at afternoon the fault indicator stopped and the status led started to flash green slowly, today it went back to the first status again, one green and one amber with normal frequency.

It will be highly appreciated if somebody help me in this.

thanks
M

5 REPLIES 5
V├нctor Cesp├│n
Honored Contributor

Re: EVA4100 Battery status is holding charge

If you check the EVA user guide, there's a table that shows you what the LEDs mean:

Status indicator Flashing + Fault indicator Flashing =
Battery is undergoing a scheduled battery load test, during which the battery is discharged and then recharged to ensure it is working properly. During the discharge cycle, you will see this display. The load test occurs infrequently and takes several hours.

Status indicator Flashing + Fault indicator Off = Battery is undergoing a full charging process.
manuj kumar
Frequent Advisor

Re: EVA4100 Battery status is holding charge

thanks vcespon for reply

i already checked the manual,

http://bizsupport1.austin.hp.com/bc/docs/support/SupportManual/c01681338/c01681338.pdf

it is noted in the table that, while load test, status flashing + fault OFF

that's why i am confused

thanks
Uwe Zessin
Honored Contributor

Re: EVA4100 Battery status is holding charge

The "Status Flashing + Fault Off" appears two times in the table - maybe that was a cut&paste error when creating the manual.
.
V├нctor Cesp├│n
Honored Contributor
Solution

Re: EVA4100 Battery status is holding charge

Check a more recent version of the manual...

http://bizsupport1.austin.hp.com/bc/docs/support/SupportManual/c01721462/c01721462.pdf

The table has been corrected.
manuj kumar
Frequent Advisor

Re: EVA4100 Battery status is holding charge

Thanks friends