- Community Home
- >
- Servers and Operating Systems
- >
- Integrity Servers
- >
- Connecting RX3600 to an APC3000 UPS
Integrity Servers
1753888
Members
7399
Online
108809
Solutions
Forums
Categories
Company
Local Language
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Discussions
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
04-28-2010 03:23 PM
04-28-2010 03:23 PM
Connecting RX3600 to an APC3000 UPS
Hello Gurus,
We will be purchasing an RX3600, running HPUX 11.31. We are wondering if this can be hooked up to an existing APC3000 UPS that is in our datacenter. The APC3000 does have a rs-232 cable. Will the RX3600 upsmond daemon be able to determine a power outage, and do a system shutdown, accordingly? Or, should we go with the "PowerTrust" UPS's?
Thanks...colin
We will be purchasing an RX3600, running HPUX 11.31. We are wondering if this can be hooked up to an existing APC3000 UPS that is in our datacenter. The APC3000 does have a rs-232 cable. Will the RX3600 upsmond daemon be able to determine a power outage, and do a system shutdown, accordingly? Or, should we go with the "PowerTrust" UPS's?
Thanks...colin
1 REPLY 1
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
04-28-2010 05:40 PM
04-28-2010 05:40 PM
Re: Connecting RX3600 to an APC3000 UPS
There are no standards for UPS products including very non-standard serial cables. Most all UPS manufacturers focus on x86 platforms with GUIs. The question is 100% UPS manufacturer. HP-UX support for UPS models such as the R3000 (aka Compaq) is quite lacking -- their download site for LanSafe software has broken links and if you manage to find the working download button, the software fails to install with several error messages.
APC provides some Javajunk to monitor the (optional) APC LAN interface but nothing for the serial port. Based on experiences with other UPS manufacturers, standard serial cables (null modem or straight through) don't work either -- you have to use the manufacturer's special cable.
For reliable shutdown prior to UPS battery exhaustion, I would only use an HP supported UPS and verify that it can actually communicate with the UPS daemon. Or use another box (Windows? Linux?) that does indeed communicate successfully with the APC box and when it's time to shutdown, setup an ssh command to trigger an orderly shutdown on the HP-UX box. And test when it is safe to do so. Don't wait for an extended power failure to find out that the HP-UX box went down hard.
Bill Hassell, sysadmin
APC provides some Javajunk to monitor the (optional) APC LAN interface but nothing for the serial port. Based on experiences with other UPS manufacturers, standard serial cables (null modem or straight through) don't work either -- you have to use the manufacturer's special cable.
For reliable shutdown prior to UPS battery exhaustion, I would only use an HP supported UPS and verify that it can actually communicate with the UPS daemon. Or use another box (Windows? Linux?) that does indeed communicate successfully with the APC box and when it's time to shutdown, setup an ssh command to trigger an orderly shutdown on the HP-UX box. And test when it is safe to do so. Don't wait for an extended power failure to find out that the HP-UX box went down hard.
Bill Hassell, sysadmin
The opinions expressed above are the personal opinions of the authors, not of Hewlett Packard Enterprise. By using this site, you accept the Terms of Use and Rules of Participation.