Hi There,

I have 2 RX7620 servers which shutdown themself recently. I checked their MP logs and found the following information.

Log Entry 2459: 07/03/2008 19:33:04
Alert level 2: Informational
Keyword: CABPWR_OFF
Cabinet Power Turned Off By Command
Reporting Entity: Power Monitor located in cabinet 0
0x4b000af800e002ac 0x01000000486d2970

Log Entry 2458: 07/03/2008 19:32:58
Alert level 2: Informational
Keyword: MAIN_BP_LPM_OFF
The main backplane is reporting the LPM status as off.
Reporting Entity: Management Processor located in cabinet 0
0x4b000ec700e002ab 0x01000000486d296a

Log Entry 2457: 07/03/2008 19:32:58
Alert level 2: Informational
Keyword: IO_BP_LPM_OFF
The IO backplane is reporting the LPM status as off.
Reporting Entity: Management Processor located in cabinet 0
0x4b000eca00e002aa 0x01000000486d296a

Log Entry 2456: 07/03/2008 19:32:58
Alert level 2: Informational
Keyword: CELL_OFF
The specified cell has been powered off.
Reporting Entity: Management Processor located in cabinet 0
Physical Location: Cell board cabinet 0 slot 1
0x44800ee800e002a8 0x00ffffffff01ff68
0x4b000ee800e002a9 0x01000000486d296a

Log Entry 2455: 07/03/2008 19:32:58
Alert level 2: Informational
Keyword: CELL_POWER_OFF
The Cell power has transitioned from an on to an off state.
Reporting Entity: Processor Dependent Hardware Controller located in cabinet 0,
slot 1
0x4b000c3901e002a7 0x01000000486d296a

Log Entry 2454: 07/03/2008 19:32:47
Alert level 2: Informational
Keyword: POWER_SWITCH_OFF
Cabinet Power Switch turned off
Reporting Entity: Power Monitor located in cabinet 0
0x4b000b1b00e002a6 0x01000000486d295f

Log Entry 2453: 07/03/2008 00:00:02
Alert level 2: Informational
Keyword: MP_TIMESTAMP
MP timestamp event.
Reporting Entity: Management Processor located in cabinet 0
0x4b001a6600e002a5 0x01000000486c1682


I don't have any clue on this. Anyone could help?

Thanks
wang & wang
6 REPLIES 6
Torsten.
Acclaimed Contributor

Re: RX7620 self shutdown.

I don't think this is a **self** shutdown:

Cabinet Power Turned Off By Command

Cabinet Power Switch turned off

Looks like somebody does it.

Hope this helps!
Regards
Torsten.

__________________________________________________
There are only 10 types of people in the world -
those who understand binary, and those who don't.

__________________________________________________
No support by private messages. Please ask the forum!

If you feel this was helpful please click the KUDOS! thumb below!   
Asif Sharif
Honored Contributor

Re: RX7620 self shutdown.

Hi kenken,

As Torsten said and log shows.

Keyword: CABPWR_OFF
Cabinet Power Turned Off By Command

Regards,
Asif Sharif
Regards,
Asif Sharif
Andrew Rutter
Honored Contributor

Re: RX7620 self shutdown.

hi,

I think you need to check who was in your server room at the time of the events?

Keyword: POWER_SWITCH_OFF
Cabinet Power Switch turned off


someone definatly turned them off, or knoocked a pdu that they run through! but above tells me that someone flicked the switch

Andy
kenken_3
Regular Advisor

Re: RX7620 self shutdown.

Thanks, Guys. I just checked my syslog.log and found this "vmunix: OS SHUTTING DOWN DUE TO A FW NOTIFICATION ON CONTROL METHOD POWER BUTTON OBJECT (PWRB) !!!!"

I tried to google it, but can't find anything. Anyone knows this?

It is a bit strange. Both of my servers were turned off. I can't find out who did this.

wang & wang
YAQUB_1
Respected Contributor
Solution

Re: RX7620 self shutdown.

Hi,

>>> It is a bit strange. Both of my servers were turned off. I can't find out who did this.
==> Some one know Ur systems MP LAN password, I am not sure is it default MP LAN Admin/Admin password. If it is then U change the password just now.

I will describe Ur previous issue:-

1. Keyword: CABPWR_OFF

Description: The +48 VDC Power was turned off by the Guardian Service Processor Command, PE, or the cabinet power switch was moved to the "OFF" position. These powers down the cabinet immediately. Thus, the critical severity level.

Cause/Action:
Cabinet switch was transitioned to "OFF".
(Some one manual power off)

Recommendation:
Cycle power switch from on to off to on.

2. Keyword: MAIN_BP_LPM_OFF

Description:
The main backplane is reporting the LPM status as off.

Cause/Action:
None

Recommendation:
None

3. Keyword: IO_BP_LPM_OFF

Description:
The main backplane is reporting the LPM status as off.

Cause/Action:
None

Recommendation:
None

4. Keyword: CELL_OFF

Description:
Physical location of the affected cell 0.
Physical location of the affected cell 1.

Cause/Action:
The cell 0 has been powered off.
The cell 1 has been powered off.

Recommendation:
None

5. Keyword: CELL_POWER_OFF

Description:
The PDHC has detected that the Cell power has transitioned from an "on" (aka "good") state to an "off" state.

Cause/Action:
The service processor has directed the Cell to power off in response to a PE command.

Recommendation:
None. This event is for informational purposes only.

6. Keyword: POWER_SWITCH_OFF

Description:
The Cabinet Power Switch was changed from the on to the off position. This may have occurred purposely. It is listed as critical since it instantly removes +48 VDC to all entities in the cabinet. +48 VDC cannot be applied until the cabinet power switch is changed to the on position.

Cause/Action:
Power switch was physically turned off. No +48 VDC Power in cabinet.

Recommendation:
Place Power Switch to on position.

7. Keyword: MP_TIMESTAMP

Description:
MP timestamp event.

Cause/Action:
None.

Recommendation:
None.

BR/
Yaqub
kenken_3
Regular Advisor

Re: RX7620 self shutdown.

it is closed.
wang & wang