RedBack
Frequent Advisor

BTU Ratings

I need to find out what the btu rating is for my family of HP servers before my A/C goes belly up.
I have LT6000r, LXR8000, LP2000r, LH3, LH3r, LPr, LXpro NetServers and A500, B132L, C360, N4000, L2000 and V2500 HP-UX.
Does someone out there have some or all of these rating?

TIA.
8 REPLIES
paul courry
Honored Contributor

Re: BTU Ratings

The basic formula for calculating the BTU rating of any equipment
is as follows:

BTU = (Watts X .95) X 3.414


As per document

A1509761


So just look at the power supply rating and get your calculator out.
RedBack
Frequent Advisor

Re: BTU Ratings

If it where only just that easy! Most of the servers do not have the wattage listed in an accessible location and the documentation/Web sites do not list wattage on most servers!!
paul courry
Honored Contributor

Re: BTU Ratings

Mark, check with your facilities department. The electricians should have a clamp-on amp meter. Just clamp this over the power cords for a second, write down the reading and multiply by volts to get Watts. If any box draws less than 1 amp (the usual lower limit for these meters) assume 1 amp.
Enes Dizdarevic
Honored Contributor

Re: BTU Ratings

For Netservers you can use tool called Rack Assistent to calculate BTU ratings: simply put the servers in the rack and rack assistent will calculate BTU (and many other things like power consuption, weight, etc.). This tool is public available: go to netserver web site (netserver.hp.com) select configuration tools, rack assistent, download it and use it.
RedBack
Frequent Advisor

Re: BTU Ratings

Thanks Paul for you help but I have been informed that if the machine is not at full power then the reading will be inaccurate as I need to calculate maximum heat dissipation.
John Clementi_1
Occasional Advisor

Re: BTU Ratings

V2500 Has a BTU of 24790 for the main box , don't forget to adin all the external drives
Great questions...really stir my brain cells
Jannett Swisher
Occasional Visitor

Re: BTU Ratings

I can answer some of your question for the servers.

Maximum Heat dissipation (BTU's/hour)
A500 1365 (440); 2048 (550)
L2000 4380 (3000 typical)
N4000 10,230 (8050 typical)
V2500 24,790
harry d brown jr
Honored Contributor

Re: BTU Ratings



Recap using Jannett's numbers:

Maximum Heat dissipation (BTU's/hour)
A500 1365 (440); 2048 (550)
L2000 4380 (3000 typical)
N4000 10,230 (8050 typical)
V2500 24,790


Stuff I found from

http://docs.hp.com/hpux/hw/index.html

and

ftp://ftp.hp.com/pub/servers/software/rackasst.exe


B132L............btus=900
C360.............btus=1708

LT6000r..........btus=2641
LXR8000..........btus=1522
LP2000r..........btus=938
LH3..............btus=2641
LH3r.............btus=2136
LPr..............btus=1041
LXpro NetServers btus=4913


live free or die
harry