BTUs - heat disipation on L and N class servers

Can anyone provide a link to where I can find the heat disipation (BTUs) for L and N class servers. I'm trying to search throughout HP and get absolutely nowhere.
4 REPLIES
harry d brown jr
Honored Contributor
Solution

Re: BTUs - heat disipation on L and N class servers

here is the L's (rp5400's)

http://www.hp.com/products1/servers/rackoptimized/rp5400series/specifications/index.html

live free or die
harry
Live Free or Die
harry d brown jr
Honored Contributor

Re: BTUs - heat disipation on L and N class servers

JHL_1
Frequent Advisor

Re: BTUs - heat disipation on L and N class servers

...that's a 10 if I ever saw one.
harry d brown jr
Honored Contributor

Re: BTUs - heat disipation on L and N class servers

John,

I'll share this with you, I just performed a requirements doc:

* N-class uses a maximum of 2429 Watts, and 13.8 Amps at 220V
...* 6 partitions per N-class, giving us 12 servers
...* With 3 in a cabinet, we would need 4 cabinets, using 24 sq feet
...* We would have a total of 29148 Watts, and 165.6 Amps
...* 99,453 Btu???s, which equates to a 8.29 tons of cooling


* rp8400 uses a maximum of 4028 Watts, and 22.9 Amps at 220V
...* 8 partitions per rp8400, giving us 9 servers
...* With 2 in a cabinet, we would need 5 cabinets, using 30 sq feet
...* We would have 36,252 Watts, and 206 Amps
...* 123,692 Btu???s, which equates to 10.31 tons of cooling


* K-class uses a maximum of 1760 watts, and 10 amps at 220V
...* 1 partition per server, giving us 72 servers
...* With 2 in a cabinet, we would need 36 cabinets, using 216 sq feet
...* We would have a total of 126,720 Watts, and 720 Amps
...* 432,369 Btu???s, which equates to 36.03 tons of cooling

* K-class servers consume 4.35 times more btu???s, amp's, and watt's than an N-class solution using Virtual Partitioning

live free or die
harry