Box 1 has a redundant power supply that is operating in degraded mode

Hi

 

 

 

We have HP StorageWork D2600 that linked to server with Smart Array P411 controller.

but Array configuration utility shows this error

StorageWorks D2600 at Port 2E : Box 1 has a redundant power supply that is operating in degraded mode

but after a few days server can not acess to storage and i can not see the Smart Array P411 controller in the Array Configuration, but after restarting server can access to the storage again

the ADUReport Attached

 

 

Thank you.

 

1 REPLY
Suman_1978
HPE Pro

Re: Box 1 has a redundant power supply that is operating in degraded mode

Hi,

 

StorageWorks D2600 at Port 2E : Box 1 Warning  Warning: One or more redundant power supplies in this enclosure has failed or is not plugged in correctly.

 

Storage Enclosure: Warning: One or more redundant power supplies in this enclosure has failed or is not plugged in correctly.
Action: Reseat the power supply firmly and check the power cable. If the problem persists, check the power supply.

 

I would suggest to check the power source or replace the power supply unit in the enclosure.

 

 

Thank You!