Re: DL360 G2 - Red Health LED when UPS powered?

 
Bill Prentice
Occasional Advisor

Re: DL360 G2 - Red Health LED when UPS powered?

Just had our maintenance guys check out the circuit.

The dedicated circuit is drawing a constant 15-17 amps. No fluctuations outside that.

Voltage from the PDU outlets is an almost constant 123.0V. The only variation occurs anywhere from 20-30 intervals and at that point the reading is 122.9V. I don't believe that fluctuation should be any issue as the wall outlet power is definitely a LOT more variable.
cnb
Honored Contributor

Re: DL360 G2 - Red Health LED when UPS powered?

Bill,

I agree something strange with the Power Supplies or something in the internal power distribution.

FYI:

http://h20000.www2.hp.com/bizsupport/TechSupport/Document.jsp?lang=en&cc=us&taskId=115&prodSeriesId=1121516&prodTypeId=15351&objectID=c01110778

Let us know what you find out.
Bill Prentice
Occasional Advisor

Re: DL360 G2 - Red Health LED when UPS powered?

We've been looking into buying at least one just to swap in and see. It's just odd that all four would do the same thing at the same time.
cnb
Honored Contributor

Re: DL360 G2 - Red Health LED when UPS powered?

Hi Bill,

Just curious if a new P/S resolved your issue?

Rgds,
Bill Prentice
Occasional Advisor

Re: DL360 G2 - Red Health LED when UPS powered?

Unfortunately that got bumped back a little with the holidays. I'm hoping to get it done in the next week or so.