HP UPS t1000 INTL with two ML350G4

Bock Markus
Frequent Advisor

HP UPS t1000 INTL with two ML350G4

Hello,

we have 2x ML350 G4 Servers and 1x HP UPS t1000 INTL with one USB and one serial Port

One server is connected by USB and works without problems.
the other server is connected by serial cable on COM1.
In the eventlog I permanent get the error message by DevManBE ID 17 "Connection lost to device"

Can anybody help me to solve this problem?

THANKS
6 REPLIES
Mauro Rusignuolo
Trusted Contributor

Re: HP UPS t1000 INTL with two ML350G4

Hi,
first installation or not?
always (before) everything rans properly?

bye.

TJK.
<> Leonardo da Vinci
Bock Markus
Frequent Advisor

Re: HP UPS t1000 INTL with two ML350G4

First installation. It's all new hardware.
Now I configured the COM1 on the server to 2400 Baud. I think that's the problem
Bock Markus
Frequent Advisor

Re: HP UPS t1000 INTL with two ML350G4

The baudrate was not the problem because the connection between ups and server works. Sometimes the connection stops for a view seconds.
How can I solve this problem?
KarloChacon
Honored Contributor

Re: HP UPS t1000 INTL with two ML350G4

hi

why dont you swap connectors between servers?
to verify if you got the same error on the other server

also do you have the latest firmware for that UPS

http://h18000.www1.hp.com/products/servers/proliantstorage/power-protection/software/hard-firmware.html?submit.y=7&submit.x=4〈=en&cc=us

regards

Didn't your momma teach you to say thanks!
Brian_Murdoch
Honored Contributor

Re: HP UPS t1000 INTL with two ML350G4

Hi,

I think you can only configure one Management Server which is connected via USB OR Serial. I don't believe you can have two diferrent Management Servers controling the UPS, which is what I think you are trying to do.

According to the Power Manager 4.1 User Guide there is no configuration which shows USB AND Serial connections.

Please see attached extract from the guide.

I think you may need to confirm this with HP. The UPS will come with both cables but you should only connect one of them I believe.

I hope this helps.

Brian
Bock Markus
Frequent Advisor

Re: HP UPS t1000 INTL with two ML350G4

That's it, what I'm thinking about. I think, I can only connect one server to the UPS.

OK THANKS