I have quite a few proliant ML350's one overnight my server rooms air condition units were both switched off my proliants just kept on rebooting themselves.

Is there a way to configure my ML350's to switch completly off when the servers are over heating ?

Thanks

G
1 REPLY
KarloChacon
Honored Contributor

Re: ML350 and heat - thermo question

hi GLEN BOWTELL

there is an option on RBSU

- F9
-server availability
- thermal shutdown, but normally is enable but default (take a look)

from here, page 19
h20000.www2.hp.com/bc/docs/support/SupportManual/c00191707/c00191707.pdf

regards