Raj77
New Member

ML570 G4 Doubts

Hi,

We are acquiring 5 ML570 G4 Servers and 42U Rack for Oracle implementation.

How many Servers are recommended per Rack. Can I put all the servers in one rack since they are 6U each?

Please reply ASAP

Best regards,

Raj
7 REPLIES 7
Rob Leadbeater
Honored Contributor

Re: ML570 G4 Doubts

Hi Raj,

Looks fairly simple to me...

5 servers @ 6U = 30U
30 is less than 42 ,so yes you can fit all servers in one rack.

If you're concerned about weight then don't be. The 10000 series rack can handle a load of up to 908kg. The maximum weight of the ML570 G4 is 62.14kg, so you're well within limits there.

Specs for the ML570 G4 are here:
http://h18004.www1.hp.com/products/quickspecs/12474_div/12474_div.html

Specs for the 10000 series 42U rack are here:
http://h18004.www1.hp.com/products/quickspecs/10995_div/10995_div.html

Hope this helps,

Cheers,

Rob
Marek Nelec
Honored Contributor

Re: ML570 G4 Doubts

Raj, ML570 G4's maximum weight is just above 62 kg (137 lb), and HP 10000 series racks support up to 909 kilos (2000 lb) - about 3 times the weight of 5 ML570 G4s. It's safe to assume that even non-HP 42 rack will support these servers, so yes, you can put all of them in one rack.
Raj77
New Member

Re: ML570 G4 Doubts

Thanks to Rob and Marek.

I would like to know what is the recommended practise considering heat problems

Raj
Marek Nelec
Honored Contributor

Re: ML570 G4 Doubts

Raj, just two best practices:
1) Check with your rack manufacturer if the rack can handle the the weight of your servers (if you have HP racks they will handle your 5 ML570 G4's).

2) Check if your floor will be able to handle the weight of your severs and and the rack.
That IMHO pretty much all.
Rob Leadbeater
Honored Contributor
Solution

Re: ML570 G4 Doubts

Hi,

The maximum heat output of a ML50 G4 is 5457 BTU/hr. If your air conditioning can cope with an additional 6 times that figure you should be ok.

Just remember to fill the remaining 12U of rack space with blanking panels to maintain the airflow correctly in the rack - the servers suck cold air in the front and blow hot air out of the back.

Cheers,

Rob