Proliant ML370G3 plus UPS

 
Liu Shaw Chan
Occasional Advisor

Proliant ML370G3 plus UPS

I have a server(HP Proliant ML370 G3) which one of the power supply connected to normal power supply & other one connected to APC Smart-UPS 2200 & configure the server with software(Powerchute).

During the power failure,the ups will call the server to shutdown when reach to battery limit.

The server is shutdown properly.But when the power back,the server won't power up automatically.Any solution for this??

1 REPLY
Rob Leadbeater
Honored Contributor

Re: Proliant ML370G3 plus UPS

Hi,

In the RBSU (BIOS) you should see an option under Server Availability for Automatic Power-On.

Make sure that is Enabled.

Hope this helps,

Regards,

Rob