- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- ProLiant Servers (ML,DL,SL)
- >
- Rack Heat Issue
ProLiant Servers (ML,DL,SL)
1753901
Members
8683
Online
108810
Solutions
Forums
Categories
Company
Local Language
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Discussions
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-04-2010 07:16 AM
05-04-2010 07:16 AM
Rack Heat Issue
We have had a couple power supplies and disk drives fail in the last month or two and we feel that it may be heat related.
We have a compaq rack with two RP3440 Servers, one MSA with 14 drives, three DL380G5 Servers, and a MSL2024.
The room is air conditioned and the rack has a fan in the top to help circulate the air.
All the systems are powered with 110V power. Would switching to 220V power make the equipment run cooler and thus less prone to failure?
Any comments or suggesions are appreciated
We have a compaq rack with two RP3440 Servers, one MSA with 14 drives, three DL380G5 Servers, and a MSL2024.
The room is air conditioned and the rack has a fan in the top to help circulate the air.
All the systems are powered with 110V power. Would switching to 220V power make the equipment run cooler and thus less prone to failure?
Any comments or suggesions are appreciated
1 REPLY 1
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
05-04-2010 02:58 PM
05-04-2010 02:58 PM
Re: Rack Heat Issue
What is the model number of the Compaq rack?
I am not familiar with the airflow requirements of the other equipment, but the DL380G5 servers require the front of the cabinet to have at least 64% open, i.e. a good deal of holes to let air in.
I use an old 22U Compaq 7000 series rack for a personal testing lab, and to make sure the servers get enough air, I have to have the front door removed.
Also, if there are gaps between the servers, the airflow will not be correct, exhaust air could recycle to the front and be taken into the server instead of the cool air. You might want to also check that the fan on top is not forcing the exhaust into the path of the cool air.
Moving to higher voltage may help as well, from what I've seen, the power supplies are much more efficient with the higher voltages and do produce less waste heat, but they are the only part that will run cooler on high voltage. (Though not by much, they already run about 89% efficient at 110, at 220 they're about 93-97%, but this varies between models)
As far as the drives, make sure you have all slots filled with either a drive or a blank, if there are gaps, the air will not flow correctly over the drives nearby, and they will not keep cool.
I am not familiar with the airflow requirements of the other equipment, but the DL380G5 servers require the front of the cabinet to have at least 64% open, i.e. a good deal of holes to let air in.
I use an old 22U Compaq 7000 series rack for a personal testing lab, and to make sure the servers get enough air, I have to have the front door removed.
Also, if there are gaps between the servers, the airflow will not be correct, exhaust air could recycle to the front and be taken into the server instead of the cool air. You might want to also check that the fan on top is not forcing the exhaust into the path of the cool air.
Moving to higher voltage may help as well, from what I've seen, the power supplies are much more efficient with the higher voltages and do produce less waste heat, but they are the only part that will run cooler on high voltage. (Though not by much, they already run about 89% efficient at 110, at 220 they're about 93-97%, but this varies between models)
As far as the drives, make sure you have all slots filled with either a drive or a blank, if there are gaps, the air will not flow correctly over the drives nearby, and they will not keep cool.
The opinions expressed above are the personal opinions of the authors, not of Hewlett Packard Enterprise. By using this site, you accept the Terms of Use and Rules of Participation.