- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- ProLiant Servers (ML,DL,SL)
- >
- Rack Power solution
ProLiant Servers (ML,DL,SL)
1752661
Members
5792
Online
108788
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Go to solution
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО04-26-2004 05:24 AM
тАО04-26-2004 05:24 AM
We use HP racks in our data center. We used to run two 20 amp circuts to each rack. This was fine for the old larger servers. Now days the small U servers pull too many amps to only run two circuts. Recently, we have tripped a few circuts by miscalculating the amperage pull required. What would be ideal is a real time amperage meter in the power strip. Is anyone aware of a good solution for rack power or a way to avoid the overload of a circuit.
The systems back up
Solved! Go to Solution.
2 REPLIES 2
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО04-26-2004 06:10 PM
тАО04-26-2004 06:10 PM
Re: Rack Power solution
We have the same problem. Not that we reach the 16 AMP (which we have) but we fear that if one circuit breaks the other one will too since all servers switch over to that circuit only (two PSU's in each server).
I think our electricians have some kind of device to simply wrap around the cable and that can measure the amps used. However I think it was thought of more using which extremely high values (like the cable going to the gigantic UPS we have) so it wasn't an option for small values like 20 amps. However you might want to check that out.
Another idea I had was to put meters in each circuit but I guess that would be expensive.
So what we did was to make sure to have a "standard" for each rack, specifying how many servers and which models to make sure we don't have this problem... But human mistakes could happened so I guess it's not best practice.
I think our electricians have some kind of device to simply wrap around the cable and that can measure the amps used. However I think it was thought of more using which extremely high values (like the cable going to the gigantic UPS we have) so it wasn't an option for small values like 20 amps. However you might want to check that out.
Another idea I had was to put meters in each circuit but I guess that would be expensive.
So what we did was to make sure to have a "standard" for each rack, specifying how many servers and which models to make sure we don't have this problem... But human mistakes could happened so I guess it's not best practice.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО04-27-2004 12:45 AM
тАО04-27-2004 12:45 AM
Solution
We have started to deploy a new Power Distribution Unit from APC that integrates an amp meter into the unit. It displays the current being drawn by the load attached and can be network attached to raise alarms if current draw exceeds thresholds. Chech this URL: http://www.apc.com/products/family/index.cfm?id=136&tab=models
The opinions expressed above are the personal opinions of the authors, not of Hewlett Packard Enterprise. By using this site, you accept the Terms of Use and Rules of Participation.