power supply

i have ups 1500 va and server ML 370G5, when the ups turn on battery, i heared a clik on the power supply of server, and when the UPS turn on elecricity the server reboot

what's wrong with this
3 REPLIES
Wayne Henegar
Frequent Advisor

Re: power supply

What model of 1500va do you have? How old is the server? I have found on newer ML350 G6 and ML370 G5 servers that I need true sine wave or double conversion UPS because the power supplies are not compatible with the cheaper UPS.
wendols
Occasional Visitor

Re: power supply

hello
My UPS is APC Smart UPS 1500VA

and my server is ML370G5 , maybe year old

thanks
Wayne Henegar
Frequent Advisor

Re: power supply

You might find some help in this forum

http://forums13.itrc.hp.com/service/forums/questionanswer.do?threadId=1393340

Some APC's don't have the correct out put, but I don't know why it would just now be showing up on a year old server. (Unless you have very stable utility and have never required the UPS to engage previously.)