R3000XR UPS

I tried to upgrade my R3000XR UPS with firmware 1.04. But now only the red Battery-LED is on. I can't turn of the UPS with the switch. Same problem when I plug out and in. And there is no communication possible with the serial port. Any suggestions?
4 REPLIES 4
Oleg Koroz
Honored Contributor

Re: R3000XR UPS

reset and run self test (see User Guide)
see if that make difference and error still stay

http://h20000.www2.hp.com/bc/docs/support/UCR/SupportManual/TPM_192131-003_rev3_us/TPM_192131-003_rev3_us.pdf

BR718573
New Member

Re: R3000XR UPS

I can press the Test/Alarm button as long as I want, nothing happens.

Ralph
Oleg Koroz
Honored Contributor

Re: R3000XR UPS

If you have no luck with reset and self-test after holding button for 5 seconds (when Unit powered) most likely Electronic Module is failed. Pull batteries Out, disconnect from wall Outlet press power ON button for 4-7 second discharge all static - place all components back - if problem still exist ├в self-test is not running, replace Electronic Module.
Electronic Module Low-Voltage 204506-001
Electronic Module High-Voltage 216097-001
BR718573
New Member

Re: R3000XR UPS

I made it like you said. Problem still exist, I really think the Electronic Module is gone. I'll replace it. Thanks for you suggestions.