- Community Home
- >
- Servers and Operating Systems
- >
- Servers - General
- >
- Re: HP Power Advisor/Power sizing for Proliant Ser...
-
- Forums
-
- Advancing Life & Work
- Advantage EX
- Alliances
- Around the Storage Block
- HPE Ezmeral: Uncut
- OEM Solutions
- Servers & Systems: The Right Compute
- Tech Insights
- The Cloud Experience Everywhere
- HPE Blog, Austria, Germany & Switzerland
- Blog HPE, France
- HPE Blog, Italy
- HPE Blog, Japan
- HPE Blog, Middle East
- HPE Blog, Russia
- HPE Blog, Saudi Arabia
- HPE Blog, South Africa
- HPE Blog, UK & Ireland
-
Blogs
- Advancing Life & Work
- Advantage EX
- Alliances
- Around the Storage Block
- HPE Blog, Latin America
- HPE Blog, Middle East
- HPE Blog, Saudi Arabia
- HPE Blog, South Africa
- HPE Blog, UK & Ireland
- HPE Ezmeral: Uncut
- OEM Solutions
- Servers & Systems: The Right Compute
- Tech Insights
- The Cloud Experience Everywhere
-
Information
- Community
- Welcome
- Getting Started
- FAQ
- Ranking Overview
- Rules of Participation
- Tips and Tricks
- Resources
- Announcements
- Email us
- Feedback
- Information Libraries
- Integrated Systems
- Networking
- Servers
- Storage
- Other HPE Sites
- Support Center
- Aruba Airheads Community
- Enterprise.nxt
- HPE Dev Community
- Cloud28+ Community
- Marketplace
-
Forums
-
Blogs
-
Information
-
English
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
01-03-2015 08:52 AM - last edited on 01-04-2015 05:26 PM by Maiko-I
01-03-2015 08:52 AM - last edited on 01-04-2015 05:26 PM by Maiko-I
HP Power Advisor/Power sizing for Proliant Servers
I am moving into a small room that I am converting into a server room. I am going to have a rack with five Proliant servers in it. Three DL360p G8's, a DL120 G7 and a ML350p G8. All of the servers have redundant power supplies of the 450 or 460 watt variety. I will also have a KVM, a small Cisco switch and a small tape drive in this rack. I currently have two independent 20 amp/120 volt circuits to the room (though I can upgrade to 30 amp circuits). I was hoping to have two UPSs, one on each circuit, and then plug each power supply on each server into a separate UPS.
I'm trying to find an adequate UPS solution for this rack. Using HP's Power Advisor I get that the total load on this setup is around 1232.93 watts / 1243.9 VA / 10.82 amps.
When I go to power calculators for other sites, I get all sorts of different numbers (mostly larger). And I have an "expert" on another forum who tells me that my actual load, at mimium, is 4.125 KVA.
What is the community's thoughts? How accurate is the HP power adviser (I would assume accurate) and how should I best plan for power?
Thanks in advance for any advice.
P.S. This thread has been moved from ProLiant Servers (ML,DL,SL) to Servers > general. - Hp Forum Moderator
- Tags:
- UPS
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
01-11-2015 11:45 AM
01-11-2015 11:45 AM
Re: HP Power Advisor/Power sizing for Proliant Servers
Hello, I can't find any HP ups calculator, lets use APC one at http://www.apc.com/tools/ups_selector/pso/rslr/index.cfm
To you setup they recomend ~2000VA UPS, count of battery packs depends on your decision how long outage you need to survive..
Jan