- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- Servers - General
- >
- Re: HP UPS Management Modul
Servers - General
1748126
Members
3268
Online
108758
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-03-2011 01:23 AM
тАО02-03-2011 01:23 AM
HP UPS Management Modul
I have a question about the Estimated Time Required To Shut Down Operating System.
If I have a system how need 2 minutes to shutdown and the ups has the runtime 10 minutes.
I get a power failure at 10:00. Start the server to shutdown 10:00 ? or start the 10:08 it need 2 minutes to shutdown?
If the power is restored is the shutdown command cancel?
/Matts
If I have a system how need 2 minutes to shutdown and the ups has the runtime 10 minutes.
I get a power failure at 10:00. Start the server to shutdown 10:00 ? or start the 10:08 it need 2 minutes to shutdown?
If the power is restored is the shutdown command cancel?
/Matts
- Tags:
- UPS
3 REPLIES 3
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-03-2011 05:58 AM
тАО02-03-2011 05:58 AM
Re: HP UPS Management Modul
It's a good idea to start at 10:02, so that you are sure that the power failure is not temporary while also being sure you have the necessary shutdown time.
The shutdown command is not going to be canceled, but you can configure the ILO to automatically power-up the server when power is restored. Anyway i don't really know if it's going to work the way you expect: i have some implementations around where i needed to switch off this feature cause it power-on servers again while still on battery power.
Give the UPS an additional battery pack to keep your server up for more than 10 minutes is also a good idea.
HTH Bye!
The shutdown command is not going to be canceled, but you can configure the ILO to automatically power-up the server when power is restored. Anyway i don't really know if it's going to work the way you expect: i have some implementations around where i needed to switch off this feature cause it power-on servers again while still on battery power.
Give the UPS an additional battery pack to keep your server up for more than 10 minutes is also a good idea.
HTH Bye!
Diego C.
MS MCSA Server 2003
HP Accredited Integration Specialist
MS MCSA Server 2003
HP Accredited Integration Specialist
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-04-2011 10:23 AM
тАО02-04-2011 10:23 AM
Re: HP UPS Management Modul
Hi,
Under Setup ---> Power Fail menu, there 2 delays parameters that you need to concern when Utility Loss:
-Shutdown Delay
-Load Shutdown Time
Shutdown Delays is the time you like the UPS while ON-Battery operating continues to power your device (avoid flickering, brown out...) just 2 to 5 minutes. Once this delay counts down to 0, a shutdown command will be issue and can't be cancelled even Utility restore shortly after that.
Load Shutdown Time is the additional delay so the UPS waits for your servers shutdown OS or run any needed script ... 3 to 5 min depend)
. After this time the UPS shut itself down
Brian
Under Setup ---> Power Fail menu, there 2 delays parameters that you need to concern when Utility Loss:
-Shutdown Delay
-Load Shutdown Time
Shutdown Delays is the time you like the UPS while ON-Battery operating continues to power your device (avoid flickering, brown out...) just 2 to 5 minutes. Once this delay counts down to 0, a shutdown command will be issue and can't be cancelled even Utility restore shortly after that.
Load Shutdown Time is the additional delay so the UPS waits for your servers shutdown OS or run any needed script ... 3 to 5 min depend)
. After this time the UPS shut itself down
Brian
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО02-09-2011 08:57 AM
тАО02-09-2011 08:57 AM
Re: HP UPS Management Modul
Hi,
Are you using HP Power Manager?
If so when power is restored shutdowns are cancelled.
There is also the option you can use 'run until battery depletion' which basically lets you run on battery for as long as you can until the UPS issues a 'battery low' warning at this point shutdown of attached systems begins. (By ticking this option it will override any delay settings you may have entered)
Hope this helps.
Mark.
Are you using HP Power Manager?
If so when power is restored shutdowns are cancelled.
There is also the option you can use 'run until battery depletion' which basically lets you run on battery for as long as you can until the UPS issues a 'battery low' warning at this point shutdown of attached systems begins. (By ticking this option it will override any delay settings you may have entered)
Hope this helps.
Mark.