- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- Servers - General
- >
- Re: Server Load Shedding using UPS Management Modu...
Servers - General
1753499
Members
4434
Online
108794
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-07-2009 07:49 AM
тАО03-07-2009 07:49 AM
Server Load Shedding using UPS Management Module
Has anyone figured out a way of shuting down non-critical servers in a c-7000 Blade Enclosure on one UPS load segment early and allowing more mission critical servers to run longer before shutting down using the HP UPS Management Module and the HP Power Protection Agents?
If I was using individual servers, I could use different load segments and just configure the shutdown parameters for the load segments differently. With Blade Servers they share common power supplies so I would have to segregate the critical and non-critical servers in different blade enclosures.
If I was using individual servers, I could use different load segments and just configure the shutdown parameters for the load segments differently. With Blade Servers they share common power supplies so I would have to segregate the critical and non-critical servers in different blade enclosures.
- Tags:
- UPS
2 REPLIES 2
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-11-2009 10:33 AM
тАО03-11-2009 10:33 AM
Re: Server Load Shedding using UPS Management Module
Hi,
You can use the SDScript (in the Add/Edit Attached Device tab, refer to UserGuide P.72). When a power loss occurred, PPA (Power Protection Agent) would be notified and then it looked for and executed the SDScript. You add a Blade shutdown command to the script on each non-critical server that you want it shutdown early. While other critical servers keep running until load-segment delays were reached...
Brian
You can use the SDScript (in the Add/Edit Attached Device tab, refer to UserGuide P.72). When a power loss occurred, PPA (Power Protection Agent) would be notified and then it looked for and executed the SDScript. You add a Blade shutdown command to the script on each non-critical server that you want it shutdown early. While other critical servers keep running until load-segment delays were reached...
Brian
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО03-11-2009 09:35 PM
тАО03-11-2009 09:35 PM
Re: Server Load Shedding using UPS Management Module
Brian,
Thanks for the suggestion but the SDScript is triggered as part of shutdown sequence.
I have the UPS Management Module configured with an Execute Command Delay of 1 minute, a Shutdown OS delay of 3 minutes and both SDScript and EventScript processing enabled. With the ShutDown Delay for the segment set to 15 minutes the observed behavior is: Run for 15 minutes after loss of incoming power (with several UPS events logged), execute SDScript, delay for 1 minute, execute system shutdown, delay for 3 minutes and power down segment.
I suppose I could use the EventScript to catch the "On Battery" event being set on the non-critical servers and shutting them down after a short delay but I was hoping for a bit more elegant solution managed directly from the UPS Management Module.
Thanks.
Thanks for the suggestion but the SDScript is triggered as part of shutdown sequence.
I have the UPS Management Module configured with an Execute Command Delay of 1 minute, a Shutdown OS delay of 3 minutes and both SDScript and EventScript processing enabled. With the ShutDown Delay for the segment set to 15 minutes the observed behavior is: Run for 15 minutes after loss of incoming power (with several UPS events logged), execute SDScript, delay for 1 minute, execute system shutdown, delay for 3 minutes and power down segment.
I suppose I could use the EventScript to catch the "On Battery" event being set on the non-critical servers and shutting them down after a short delay but I was hoping for a bit more elegant solution managed directly from the UPS Management Module.
Thanks.