- Community Home
- >
- Networking
- >
- Legacy
- >
- Switches, Hubs, Modems
- >
- 2626 reboots and Cold Equipment Rooms
Switches, Hubs, and Modems
1752359
Members
6318
Online
108787
Solutions
Forums
Categories
Company
Local Language
юдл
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
юдл
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО01-27-2006 08:42 AM
тАО01-27-2006 08:42 AM
2626 reboots and Cold Equipment Rooms
Has anyone else had problems with your 2626 (J4900B) switches in cold enviroments? I have two switches that have been randomly rebooting when the temp drops in rooms where 2626 switches are located. I move the switches to my office (70F) and they have no problems. Move them back to the cold and they start rebooting.
Temp range is well within the spec, it ranges from 40F - 70F. With the switches having problem during the colder part of the day.
Support said they have had only one other case like this in Europe. I can't be the only other person.
Temp range is well within the spec, it ranges from 40F - 70F. With the switches having problem during the colder part of the day.
Support said they have had only one other case like this in Europe. I can't be the only other person.
2 REPLIES 2
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО01-31-2006 08:32 AM
тАО01-31-2006 08:32 AM
Re: 2626 reboots and Cold Equipment Rooms
Hi Drew,
How cold is the room? I have had the switches in a comm closet that sometimes got as low as 62F and have never had a problem.
My first guess would be a bad solder connection somewhere internally - there could be a loose lead that changes position when the temperature changes. The 70F office environment may be just warm enough to make things work. I guess the cooling fans are just too efficient - it would be nice if they would shut off when the temp is low enough.
Allan in Atlanta
How cold is the room? I have had the switches in a comm closet that sometimes got as low as 62F and have never had a problem.
My first guess would be a bad solder connection somewhere internally - there could be a loose lead that changes position when the temperature changes. The 70F office environment may be just warm enough to make things work. I guess the cooling fans are just too efficient - it would be nice if they would shut off when the temp is low enough.
Allan in Atlanta
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО01-31-2006 08:44 AM
тАО01-31-2006 08:44 AM
Re: 2626 reboots and Cold Equipment Rooms
Shalom Drew,
If the device is failing in temperature senstive situations within operating specifications, it is likely to fail completely at some point.
I'd recommend having it serviced or replaced. Its not uncommon for devices to not meet their operating specifications, but if you are going to rely on this machine, it must be serviced.
It may be a manufacturing problem and you may indeed be one of two people with this issue. Have them replaced, eventually, probably out of warranty the switch will fail or develop new quirks.
SEP
If the device is failing in temperature senstive situations within operating specifications, it is likely to fail completely at some point.
I'd recommend having it serviced or replaced. Its not uncommon for devices to not meet their operating specifications, but if you are going to rely on this machine, it must be serviced.
It may be a manufacturing problem and you may indeed be one of two people with this issue. Have them replaced, eventually, probably out of warranty the switch will fail or develop new quirks.
SEP
Steven E Protter
Owner of ISN Corporation
http://isnamerica.com
http://hpuxconsulting.com
Sponsor: http://hpux.ws
Twitter: http://twitter.com/hpuxlinux
Founder http://newdatacloud.com
Owner of ISN Corporation