Re: shutdown completely an HP-UX server

 
SOLVED
Go to solution
Pete Randall
Outstanding Contributor
Solution

Re: shutdown completely an HP-UX server

Ettore,

Oh, that's what you were asking! ;^)

Depending on your ups monitor, you may well have the option to specify whether it will come back on after the power is restored. See the man page for ups_conf and specifically the parameter "kill_after_shutdown".


Pete

Pete
Steven E. Protter
Exalted Contributor

Re: shutdown completely an HP-UX server

If this is happening unexpectedly it should be in the GSP log, some kind of problem.

We have run the unplug shutdown tests and seen the systems come down with a shutdown -h 0


This works if ups_mond.conf is set up properly.

This does not shut the ups itself down. That we have to do with the switches on the front.

SEP
Steven E Protter
Owner of ISN Corporation
http://isnamerica.com
http://hpuxconsulting.com
Sponsor: http://hpux.ws
Twitter: http://twitter.com/hpuxlinux
Founder http://newdatacloud.com
Fabio Ettore
Honored Contributor

Re: shutdown completely an HP-UX server

Good morning guys,

thanks Pete and SEP. Your suggestion on UPS configuration is really interesting. I will let you know progresses about this issue.

Best regards,
Ettore
WISH? IMPROVEMENT!
Fabio Ettore
Honored Contributor

Re: shutdown completely an HP-UX server

Pete and SEP, a question for you (and of course for ITRC people too):
If UPS dies and server with its configuration together then how does UPS know the option kill_after_shutdown, that is UPS must be turned OFF when AC line voltage comes back?

Best regards,
Ettore
WISH? IMPROVEMENT!
Bill Hassell
Honored Contributor

Re: shutdown completely an HP-UX server

The behavior of the UPS during a power failure where the batteries run out is very dependent on the model of the UPS and whether it has non-volatile RAM to remember optional settings. In the case of battery exhaustion, having the UPS come back up is seldom the right choice, especially if there are related services (like networking) that are on a separate UPS (or no UPS at all). Complete loss of power really needs humans to power things back on (like big disk arrays, tape changers, etc).


Bill Hassell, sysadmin
Fabio Ettore
Honored Contributor

Re: shutdown completely an HP-UX server

Thanks Bill, thanks everybody for your responses and your experiencies.

Like Robik says: Ettore, ITRC forum is way COOL!
Oh....he is right! :-)

Best regards,
Ettore

P.S.: Robik, are you happy? I am advertising https://www.beepz.com/chatzone
WISH? IMPROVEMENT!
Fabio Ettore
Honored Contributor

Re: shutdown completely an HP-UX server

ok
WISH? IMPROVEMENT!