- Community Home
- >
- Servers and Operating Systems
- >
- HPE BladeSystem
- >
- BladeSystem - General
- >
- Re: 2 new c7000s - fans blowing at 89% - why?
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-23-2009 05:58 PM
тАО11-23-2009 05:58 PM
2 new c7000s - fans blowing at 89% - why?
We've populated 2 c7000s with 10 BL460 G6s each and spread them out. In the third c7000, it is populated with 3 x BL460 G5 (old ones), to be populated a little later with newer G6s.
We've upgraded the OAs to 2.60 for all three enclosures. For some reason, the 2 c7000s with the G6s have ALL the fans blowing at 89%.
No reason why - the ambient temperature is 17C & 19C respectively.
None of our fully loaded c7000s are close. Sounds like a jet engine in our data centre just from these 2 enclosures, and that's saying something.
Has anyone seen this? Could it be a OA firmware issue? I haven't upgraded to 2.60 on any of the old enclosures.
Any help is appreciated...
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-24-2009 07:34 AM
тАО11-24-2009 07:34 AM
Re: 2 new c7000s - fans blowing at 89% - why?
Have you updated the Power Management controller firmware on the G6 Blades as well as the iLo firmware?
I think you can get all this at hp.com/go/support and search BL460 g6
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-24-2009 11:16 AM
тАО11-24-2009 11:16 AM
Re: 2 new c7000s - fans blowing at 89% - why?
Have reseated both OAs as well.
Logged a call to HP, but haven't seen anything yet.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-28-2009 03:40 PM
тАО11-28-2009 03:40 PM
Re: 2 new c7000s - fans blowing at 89% - why?
hi willy ,
first ensure no blanking plates are missing,
from blade slots or power supply slots as these fans are designed on a closed enclosure for optimal airflow..
take all firmwares as it is ultimately the OA that manages the enclosure , not the individual blades but blades need firmwares inplace too use guide below
http://h18004.www1.hp.com/products/blades/components/c-class.html#tab3_content
then give oa reboot command from cli when all done and should be okay
enjoy :)
This is how we thank in the forum
http://forums11.itrc.hp.com/service/forums/helptips.do?#33
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 09:30 AM
тАО11-30-2009 09:30 AM
Re: 2 new c7000s - fans blowing at 89% - why?
Thanks for the advice - I'll assign points later, but I'll give an update to the issue.
The two enclosures are Gen 2 c7000s. Might be a firmware issue with the OA.
Found the cause of the fans blowing at 89%. A number of servers had the virtual fan blowing at 100% (see attached bitmap). You can see it by going to the Web Admin for the iLO of the blade, and then looking at the System Info/Fan tab.
To fix the issue, I simply reset the iLO within Diagnostics.
However, everytime I reboot these particular servers, the fan kicks in again to 100%. I then again reset the iLO to make it go back to normal.
Peculiar to say the least. Working with HP to figure out what is going on. Reseating the blades don't help. I may reflash the firmware of the iLOs first to see if it helps. Just haven't had the time yet.
Will keep everyone posted!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 10:19 AM
тАО11-30-2009 10:19 AM
Re: 2 new c7000s - fans blowing at 89% - why?
http://www11.itrc.hp.com/service/cki/docDisplay.do?docLocale=en&docId=emr_na-c01113006-14
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 11:23 AM
тАО11-30-2009 11:23 AM
Re: 2 new c7000s - fans blowing at 89% - why?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 11:53 AM
тАО11-30-2009 11:53 AM
Re: 2 new c7000s - fans blowing at 89% - why?
OA f/w is up-to-date at 2.60.
I reflashed the f/w on one of the blades with the issue, but it didn't help. As soon as I reboot it, the fan kicks up again.
Awaiting a response from HP.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 02:36 PM
тАО11-30-2009 02:36 PM
Re: 2 new c7000s - fans blowing at 89% - why?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
тАО11-30-2009 03:37 PM
тАО11-30-2009 03:37 PM
Re: 2 new c7000s - fans blowing at 89% - why?
many peopleonly update some firmwwares , on some blades and issue persists , this is because the 0A dynamically administers the enclosure and ift does not work well with differant , mixed firmwares especially if the blades are the same generation seen this many times ..
first update all sys boards then all ilo
then send reboot command to OA from cli all fans will spin up full speed, this is normal they will fall back in circa 60 seconds ,
now see if issue happens again ,,