BL460 Power Enclosure Error

Recently we've started getting notifications in event viewer with the following error:

Machine Environment : Power Enclosure Overheating (Zone 2, Location Power Supply, Temperature 201C, Enclosure Address FC97)

10 seconds later it seems to resolve itself and sends out a second notifier:

NOTE: This event indicates that the following situation, which was previously logged as an error, has been REPAIRED and is no longer a problem.

3 REPLIES 3
Dave Zegen
New Member

Re: BL460 Power Enclosure Error

Update:

Here is an email notification we recieve-

Title: cpqRackPowerSubsystemLineVoltageProblem

Trap Description: "The rack power supply detected an input line voltage problem.

User Action: Check the power input for the power supply or replace any failed power supplies as soon as possible."
Service Action:
The power supply at position 1 of power supply enclosure Unknown has suffered a loss of line voltage. Inspect power supply connections and take necessary action to restore power.

Failing Part:
Power Supply Position: 1
Power Supply Enclosure: Unknown

Failing Part Location:
The power supply that lost line voltage is installed at position 1 of power supply enclosure Unknown in the rack enclosure Unknown a ProLiant BL20p G3 with serial number USM52602H4.

Service Notes:


Power Supply Spare Part #: undefined
Power Supply Position: 1
Power Supply Enclosure: Unknown

Rack Enclosure Model #: ProLiant BL20p G3
Rack Enclosure Name: Unknown
Rack Enclosure Serial #: M019NFH14W
Rack Enclosure ProductID: 380634-B21
Rack Enclosure FW Rev: undefined
Jimmy Vance
HPE Pro

Re: BL460 Power Enclosure Error

So are you dealing with power error messages from 2 different enclosures? Your thread title is for a BL460, your second message looks to be from the older enclosures for the BL20p. BL460 and BL20p servers use different enclosures
No support by private messages. Please ask the forum! 
Blazhev_1
Honored Contributor

Re: BL460 Power Enclosure Error

Hi,

this is known issue with the p-class management module firmware

http://h20000.www2.hp.com/bizsupport/TechSupport/SoftwareDescription.jsp?lang=en&cc=us&prodTypeId=3709945&prodSeriesId=397630&swItem=MTX-9e0e8e80b2d545eeaa26c38678&prodNameId=3288174&swEnvOID=1005&swLang=8&taskId=135&mode=5


Check revision history (Fixes) :

Enhanced error detection algorithm to prevent false power enclosure overheating messages from being posted in the IML log on 1U power enclosures.
Caution: Machine Environment: "Power Enclosure Overheating (Zone X, Location Power Supply, Temperature xxxC, Enclosure Serial Number xxxxxxxxxx"
Repaired: Machine Environment: "Power Enclosure Overheating (Zone X, Location Power Supply, Temperature 0C, Enclosure Serial Number xxxxxxxxxx"

Update and error will go away

Regards