Can a 3 phase c7000 be converted to single phase power?

 
Highlighted
Occasional Contributor

Can a 3 phase c7000 be converted to single phase power?

I have a 3 phase c7000 enclosure and want to see if it can be converted to single phase. All of the documentation for the c7000 seem to show that everything (part #s) between the 3 phase and the single phase enclosure are the same, with the exception of the power module that holds the power supplies.

I can order the single phase power module and swap them out, but is that all there is to it?

The single phase power module part number is: 413379-B21

Thanks,
3 REPLIES 3
Highlighted
Honored Contributor

Re: Can a 3 phase c7000 be converted to single phase power?

Hi Brandon,

yes you can swap them thats all you need to Do. There are no additional parts needed.

You have mentioned the part number of the module as 413379-B21, i think this is wrong.

Please visit the below link, In Page 24 they mention a different part number.
The Correct part Number of the device is 413494-001.

Do verify the same.
http://h20000.www2.hp.com/bc/docs/support/SupportManual/c00714237/c00714237.pdf?jumpid=reg_R1002_USEN


Regards,
Raghuarch

Highlighted
Occasional Contributor

Re: Can a 3 phase c7000 be converted to single phase power?

Great news! Thanks Raghuarch for your help.
Highlighted
Honored Contributor

Re: Can a 3 phase c7000 be converted to single phase power?

Hi,

Both numbers are for the same part.
413379-B21 is the optional, with it you can order, the other one is the spare with it you can replace old one.
You can check it at www.partsurfer.hp.com

Regards,

Pac