Re: HP c7000 blade enclosure fans

 
SOLVED
Go to solution
Jeff Speroff
Occasional Contributor

HP c7000 blade enclosure fans

Hello,

My customer has three blade enclosures in one rack in a temperature controlled data center.  The bottom enclosure's fans are running twice as fast as the other two.  72%-85% for enclosure in question.  Others in same rack running at 31%-52%.

There are 14 BL 460c G10 blades. The empty two bays have caps for proper air flow.  All of them are running the same firmware, not necessarily the newest.  (Customer is  resistant to upgrading firmware unless absolutely needed.  Always tells me that every other server or enclosure is running fine without a firmware upgrade).

Any help appreciated.

2 REPLIES 2
Jeff Speroff
Occasional Contributor

Re: HP c7000 blade enclosure fans

Hello,

Update:

Created case with HP.  They recommended running an OA show all report and submitting to tech support.  They would then be able to pinpoint server or compnent problem.

AmRa
HPE Pro
Solution

Re: HP c7000 blade enclosure fans

Hello,

Generate OA SHOWALL report from working enclosure and enclosure in question.

Compare SHOW ENCLOSURE TEMP from both OA SHOWALL report.  This will help you to identify which device causing the issue.

Example :

>SHOW ENCLOSURE TEMP

Locale Bay # Temp Status Temp Caution Critical
---------------------- ----- ----------- -------- ------- --------
Enclosure N/A 18C/ 64F --- ---
Onboard Administrator 1 OK 29C/ 84F 75C 80C
Onboard Administrator 2 OK 29C/ 84F 75C 80C
Blade Bay 1 N/A 15C/ 59F 42C 46C
Blade Bay 2 N/A 16C/ 60F 42C 46C
Blade Bay 3 N/A 16C/ 60F 42C 46C
Blade Bay 4 N/A 16C/ 60F 42C 46C
Blade Bay 5 N/A 15C/ 59F 42C 46C
Blade Bay 6 N/A 17C/ 62F 42C 46C
Blade Bay 7 N/A 18C/ 64F 42C 46C
Blade Bay 8 N/A 17C/ 62F 42C 46C
Blade Bay 9 N/A 15C/ 59F 42C 46C
Blade Bay 10 N/A 16C/ 60F 42C 46C
Blade Bay 11 N/A 16C/ 60F 42C 46C
Blade Bay 12 N/A 17C/ 62F 42C 46C
Blade Bay 13 N/A 17C/ 62F 42C 46C
Blade Bay 14 N/A 16C/ 60F 42C 46C
Blade Bay 15 N/A 16C/ 60F 42C 46C
Blade Bay 16 N/A 17C/ 62F 42C 46C
Interconnect Module 1 OK ---- --- ---
Interconnect Module 2 OK ---- --- ---
Interconnect Module 3 OK ---- --- ---
Interconnect Module 4 OK ---- --- ---

 

Steps to generate OA SHOWALL report:

1) Login into the OA as administrator
2) Go to enclosure settings
3) Click on configuration scripts
4) In the middle panel of the page Click on SHOW ALL.
4) Please allow it to complete it will take a few minutes to run .
5) Copy and paste into notepad
6) Save as notepad file as OASHOWALL.txt

If still unable to identify the issue then request you to please raise support ticket with HPE support team for further assistance.

I am an HPE Employee.
[Any personal opinions expressed are mine, and not official statements on behalf of Hewlett Packard Enterprise]

Accept or Kudo