chassis temperature thresholds

 
SOLVED
Go to solution
Michal Toth
Regular Advisor

chassis temperature thresholds

HI all,

envd works with two threshold levels for environmental temperature : critical and emergency (OVERTEMP_EMERG and OVERTEMP_CRIT). By default, when emergency threshold is reached, envd issues a shutdown. As far as I understand it correctly, envd reads events directly off the hardware (propably GSP/MP), but I was unable to find out how to translate these symbolic thresholds into absolute value of Celsius grades and perhaps how to increase/decrease particular threshold levels. Hints on this one are more than welcome.

regards

Michal
4 REPLIES 4
Solution

Re: chassis temperature thresholds

I'm not sure whether this changes from model to model, but in general terms:

OVERTEMP_CRIT = over 30 degrees Celsius

OVERTEMP_EMERG = over 34 degrees Celsius - the usual response to this is for envd to complete a graceful shutdown

There's another event at about 40 degrees Celsius which will cause the platform monitor to just remove DC power to the system (non graceful halt), but unless temperatures go up VERY quickly you shouldn't reach that one.

You can't change any of these values - nor should you even attempt to - HP have determined the safe operating envelopes for the systems, changing them would probably invalidate warranty.

Of course it goes without saying that temperature sensor in servers are not sensible methods of determining ambient temperature in your datacentre.

HTH

Duncan

I am an HPE Employee
Accept or Kudo

Re: chassis temperature thresholds

I should also have added that the temperature is measured on airflow *in* to the system rather than airflow *leaving* the system.

HTH

Duncan

I am an HPE Employee
Accept or Kudo
Steven E. Protter
Exalted Contributor

Re: chassis temperature thresholds

Shalom Michal,

Changing the threasholds is a bad idea. These systems are though, but operating them outside normal temperature will eventually do serious damage to them.

SEP
Steven E Protter
Owner of ISN Corporation
http://isnamerica.com
http://hpuxconsulting.com
Sponsor: http://hpux.ws
Twitter: http://twitter.com/hpuxlinux
Founder http://newdatacloud.com
Michal Toth
Regular Advisor

Re: chassis temperature thresholds

thank you all

temperature thresholds are hardwired