What kind of power cord I need to use for a HP ProLiant DL585 G1

 
SOLVED
Go to solution
IVAN JUNCO
New Member

What kind of power cord I need to use for a HP ProLiant DL585 G1

I just want to know what kind of power cord I need to use for a HP ProLiant DL585 G1. On the back of the power supply says 16A 250V; this means that I have to connect the power cord in a 250V source? How can i convert this to 120V?

Ivan
4 REPLIES 4
Matti_Kurkela
Honored Contributor
Solution

Re: What kind of power cord I need to use for a HP ProLiant DL585 G1

16A and 250V are the nominal maximum values the power supply can handle.

According to the QuickSpecs document, the system can accept anything from as low as 90 volts up to 264 volts.

http://h18006.www1.hp.com/products/quickspecs/11902_div/11902_div.HTML#Power Specifications

The power table indicates that on 115V, this server will take a nominal current of 10.4A, so you should pick a cable that is thick enough to handle at least 10A of current without heating up.

MK
MK
IVAN JUNCO
New Member

Re: What kind of power cord I need to use for a HP ProLiant DL585 G1

I'm having too much trouble to find the HP Proliant DL585 power cable. I'm looking for something compatible with any 120V USA plog. Any one knows where I can get that?
Matti_Kurkela
Honored Contributor

Re: What kind of power cord I need to use for a HP ProLiant DL585 G1

This page might help:

http://h18004.www1.hp.com/products/servers/proliantstorage/bcs-rackandpower/power-management/cordsets.html?jumpid=reg_R1002_USEN

Disclaimer: I'm not very familiar with US power sockets. My information comes from here:
http://en.wikipedia.org/wiki/Wall_socket

In general, you'll need power cords that will handle the _maximum_ this system can draw. This is to avoid the danger of cables overheating and burning in case one of the PSUs fails and all the power needed by a maximally-configured DL585 goes through just one cable.

Based on these two web pages, you would seem to need HP E7802A cables and NEMA 2-20 or NEMA 5-20 sockets to plug them into. The different socket type guarantees that the wiring from the socket to the circuit breaker and the breaker itself is adequately sized for the load.

Consult your local electrician for more information, if necessary.

MK
MK
James Joost
Advisor

Re: What kind of power cord I need to use for a HP ProLiant DL585 G1

HI

The DL585G1 can be plugged into a standard 120v power outlet.

The power cord you need is a
Nema 5-15P to IEC320-C19.

The nema 5-15p is a convention 120volt three prong plug.

At the server end, the C19 is a slightly bigger plug than the C13 that are normally on desktop systems.

The HP part numbers are
option # 235603-001
spare part # 237457-001

Even if you can't get then from HP, this type of power cord is eash to find, just make sure it is rated for at least 12A