- Community Home
- >
- Servers and Operating Systems
- >
- HPE ProLiant
- >
- Server Management - Systems Insight Manager
- >
- cpqHeThermalDegradedAction
Categories
Company
Local Language
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Discussions
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Community
Resources
Forums
Blogs
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
08-20-2012 12:33 AM
08-20-2012 12:33 AM
cpqHeThermalDegradedAction
Hi at all,
I installed in my envinroment HP sim 6.2. I have 2 servers HP: proliant ML570 G4 and proliant ProLiant DL360 G7 monitored by sim.
When in server room I had a problem with system cooling I received error snmp from ML570 G4:
Event Name: (SNMP) Thermal Status Degraded (6041)
URL: xxxxxxxxxx:2381/
Event originator: my ML570 G4 server
Event Severity: Critical
Event received: 02-Aug-2012, 18:05:40
Event description: The temperature status has been set to degraded in the specified chassis and location. The server``s temperature is outside of the normal operating range. The server will be shutdown if the
cpqHeThermalDegradedAction variable is set to shutdown(3).
firs question: Why I received only snmp trap temperature from proliant ML570, while I didn't receive message from ProLiant DL360?
second question: Could I set sim to specific threshold for all servers? For example I want receive snmp temperature message when the temperature is above 37°C?
thanks
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
08-21-2012 07:40 AM
08-21-2012 07:40 AM
Re: cpqHeThermalDegradedAction
You need to check the event log on the DL to see if an event was actually logged. Secondly, to my knowledge you cannot set a thermal warning threshold in SIM. SIM simply reacts to the criticality of this type of event.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
08-22-2012 12:15 AM
08-22-2012 12:15 AM
Re: cpqHeThermalDegradedAction
Ok,
Too me think that is not possible set a specific threshold.
Thanks for your post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
09-23-2012 10:43 PM
09-23-2012 10:43 PM
Re: cpqHeThermalDegradedAction
Hi Luca,
Re: Question 1:
There is a reasonable chance that the thermal thresholds between the two servers are different and by design. I would suggest doing an SNMPwalk of the thermal MIBS which start at: 1.3.6.1.4.1.232.6.2.6.1.0
The Temperature sensor readings are at 1.3.6.1.4.1.232.6.2.6.8.1.4.0.1
4.0.1 = ioBoard
4.0.2 = ambient
4.0.3 = CPU 1 core 1
4.0.4 = CPU 1 Core 2
Re: Question 2
When I asked the question of HP some time ago, I was advised that HP hard code the thresholds and they do this to ensure modification does not occur which would void warranty. To that end, HPSIM relies on SNMP Traps for thermal alerts.