- Community Home
- >
- Servers and Operating Systems
- >
- Legacy
- >
- Netservers
- >
- Re: Heat Generated
Netservers
1759410
Members
2962
Online
108882
Solutions
Forums
Categories
Company
Local Language
back
Forums
Discussions
Forums
- Data Protection and Retention
- Entry Storage Systems
- Legacy
- Midrange and Enterprise Storage
- Storage Networking
- HPE Nimble Storage
Discussions
Discussions
Discussions
Forums
Discussions
back
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
- BladeSystem Infrastructure and Application Solutions
- Appliance Servers
- Alpha Servers
- BackOffice Products
- Internet Products
- HPE 9000 and HPE e3000 Servers
- Networking
- Netservers
- Secure OS Software for Linux
- Server Management (Insight Manager 7)
- Windows Server 2003
- Operating System - Tru64 Unix
- ProLiant Deployment and Provisioning
- Linux-Based Community / Regional
- Microsoft System Center Integration
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Discussion Boards
Blogs
Information
Community
Resources
Community Language
Language
Forums
Blogs
Topic Options
- Subscribe to RSS Feed
- Mark Topic as New
- Mark Topic as Read
- Float this Topic for Current User
- Bookmark
- Subscribe
- Printer Friendly Page
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
06-24-2002 01:29 AM
06-24-2002 01:29 AM
Heat Generated
Hi,
I have couple of HP netserver LC 2000 and LH 3000 servers in my computer room, The temperature in my computer room has raised from 20 degrees from 25 degrees due to additional server equipment installed recently, We are planning to install additional Aircondition in the server room, but my management want to know the amount of heat generated by each server. Is there a way I can find out how much heat each server genarates.
Please help.
Thank you
I have couple of HP netserver LC 2000 and LH 3000 servers in my computer room, The temperature in my computer room has raised from 20 degrees from 25 degrees due to additional server equipment installed recently, We are planning to install additional Aircondition in the server room, but my management want to know the amount of heat generated by each server. Is there a way I can find out how much heat each server genarates.
Please help.
Thank you
Arun Aroza
1 REPLY 1
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Report Inappropriate Content
06-24-2002 03:02 AM
06-24-2002 03:02 AM
Re: Heat Generated
LC2000 - 1843 BTUs per hour
LH3000 - 2641 BTUs per hour
In general, find out what is the maximum input power consumption of a server (in Watts) and multiply that value by 3.413 to calculate the maximum heat generation in BTUs (British thermal units) per hour.
1 BTU equals approx. 252 calories or 1055 joules.
HTH,
Marcin
LH3000 - 2641 BTUs per hour
In general, find out what is the maximum input power consumption of a server (in Watts) and multiply that value by 3.413 to calculate the maximum heat generation in BTUs (British thermal units) per hour.
1 BTU equals approx. 252 calories or 1055 joules.
HTH,
Marcin
The opinions expressed above are the personal opinions of the authors, not of Hewlett Packard Enterprise. By using this site, you accept the Terms of Use and Rules of Participation.